8 Bolts Stiffened End Plate Connection Design
The 8 Bolts Stiffened End Plate Connection is a type of moment-transmitting connection (rigid connection), which is bolted to the columns and welded to the beam, and is a stiffening plate. Bolt control, weld control, plate control and connection application limits control are performed automatically according to the placement of the elements of the connection. The 8 bolts stiffened end plate connection design is made automatically according to the Design, Calculation and Construction Principles of Steel Structures (ÇYTHYEDY) or AISC 360-16 regulations and the connection report is created. Connection detail application limits are checked according to TBDY Table 9B.1.
In the calculation of the 8 Bolts Stiffened End Plate Connection, horizontal and vertical bolt distances, end plate weld thickness, continuity plate weld thickness and application limits are checked under geometry control. In strength checks, bolt diameter, end plate thickness, end plate shear yield, end plate shear failure, reinforcement plate weld thickness, slip on support bolts, bolt hole crush on end plate, bolt hole crush on column head, butt plate weld thickness, column head thickness, column panel zone slip and slip zone thickness control.
Connection Geometry
Geometry Checks
Bolt Spacing
smin ≥ 3d
ÇYTHYEDY 13.3.6
s
90 mm
d
30 mm
s =90 mm > smin = 3*30=90 mm
Horizontal Edge Distance
Leh ≥ Le- min
ÇYTHYEDY 13.3.7
Leh
60 mm
L eh ≥ 2d = 2 * 30 = 60 mm conformity check for application
Le- min
40 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance
Lev ≥ Le- min
ÇYTHYEDY 13.3.7
Lev
60 mm
Le- min
40 mm
Beam Web to End Plate Weld Size
a ≥ amin
a
5 mm
amin
3.5 mm
Table 13.4
Stiffener to Beam Flange Weld Size
a ≥ amin
a
6 mm
amin
4 mm
Table 13.4
Stiffener to End Plate Weld Size
a ≥ amin
a
6 mm
amin
4 mm
Table 13.4
a ≥ amin
a
8 mm
amin
4 mm
Table 13.4
a ≥ amin
a
8 mm
amin
4 mm
Table 13.4
Connection Detail Prequalification Limits (TBDY Table 9B.1)
Beam span / Beam cross-section height
9144 mm /450 mm=20.32
≥7.0
End plate thickness, tp
30 mm
18≤t p ≤65
Flange plate width, bp
298 mm
215≤ b p ≤ 400
Horizontal distance between bolts, g
154 mm
125≤g≤155
pfi
72 mm
40≤p fi ≤50
pfo
72 mm
40≤p fi ≤50
Beam cross section height, db
450 mm
450≤ d b ≤ 950
Beam head thickness, tbf
15 mm
14≤t bf ≤35
Column cross section height
650
≤ 920 mm
Bolt class
10.9
8.8 - 10.9
Min yield stress of the frontal plate material
275 MPa
235 /275/355 MPa
Flange plate weld
CJP
CJP
Strength Checks
Bolt Diameter
Muc
833.213 kNm
AISC 358-16 (6.8-4)
Ft
750000 kN/m2
h1
h2
h3
h4
db
Required
Available
Rate
Control
22.252 mm
30 mm
0.708
End Plate Thickness
Muc
833.213 kNm
AISC 358-16 (6.8-5)
Fyp
275000 kN/m2
s
Yp
Yp
tp
Required
Available
Ratio
Control
23.01 mm
30 mm
0.767
End Plate Stiffener Thickness
tbw
9 mm
AISC 358-16 (6.8-9)
Fyb
275000 kN/m2
Fys
275000 kN/m2
ts
12 mm
Required
Available
Ratio
Control
9 mm
15 mm
0.600
End Plate Stiffener Local Buckling
hs
210 mm
AISC 358-16 (6.8-10)
ts
15 mm
E
205939650 kN/m2
Fys
275000 kN/m2
Required
Available
Rate
Control
14 mm
15.325 mm
0.914
Fys
275000 kN/m2
AISC DG 4-2nd
3.2.10
ts
15 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
7.938 mm
8.487 mm
0.935
Fys
275000 kN/m2
AISC DG 4-2nd
3.2.10
ts
15 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
7.938 mm
8.487 mm
0.935
Bolt Shear at Support
Ab
Fn
Rn
ΦRn
Required
Available
Ratio
Control
211.464 kN
2290.22 kN
0.092
Bolt Bearing on End Plate
dh
30+3=33 mm
Lc,edge
Rn
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Rn-edge
Lc,spacing1
Rn-spacing1
Lc,spacing2
Rn-spacing2
Rn
ΦRn
Required
Available
Ratio
Control
211.464 kN
6044.22 kN
0.035
Bolt Bearing on Column Flange
dh
30+3=33 mm
Rn
ÇYTHYEDY 13.3.13
Rn-edge
Lc,spacing1
Rn-spacing1
Lc,spacing2
Rn-spacing2
Rn
ΦRn
Required
Available
Ratio
Control
211.464 kN
6424.142
0.033
Fyp
275000 kN/m2
AISC 358-16
(6.7.6) 3
tbw
9 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
4.763 mm
7.072 mm
0.673
Column Flange Thickness
Muc
803.836 kNm
AISC 358-16 (6.8-13)
Fyp
275000 kN/m2
s
c
Yc
Yc
tcf
Required
Available
Ratio
Control
21.772mm
31 mm
0.702
Column Panel Zone Shear
Pr
429,124 kN
ÇYTHYEDY 13.29a
Py
Fy
275000 kN/m2
Ag
28634.759 mm2
dc
650 mm
tw
16 mm
Rn
ΦRn
Required
Available
Ratio
Control
1696.742 kN
1716 kN
0.989
Panel Zone Thickness
t min ≥u / 180
TBDY 2018 9.3.4.2b
tmin = t w
16 mm
tw
16 mm
u
2016 mm
Required
Available
Ratio
Control
11.2 mm
16 mm
0.700