Welded Flange Plate Connection Design per AISC 360-16
How does ideCAD design Welded Flange Plate Connections according to AISC 360-16?
  • Design limit states of welded flange plate connections are calculated automatically according to AISC 360-16.
Ag: Gross area
An: Net cross-section area
Aw: Cross-section web area
bp = width of end-plate, in. (mm)
g = horizontal distance between bolts, in. (mm)
dh: Bolt hole diameter
nsp: Number of slip planes
K: Effective length factor
L: Connector distance
tbf = thickness of beam flange, in. (mm)
w = Size of weld leg, in. (mm)
Rn: Characteristic strength
Rnwl: Total nominal strength of longitudinally loaded fillet welds
Rnwt: Total nominal strength of transversely loaded fillet welds,
Connection Geometry
GEOMETRY CHECK
Flange Plate to Beam Flange Weld Size
w ≥ wmin
w
11.315 mm
wmin
6 mm
Table J2.4
Shear Plate to Beam Web Weld Size
w ≥ wmin
w
11.315 mm
wmin
5 mm
Table J2.4
Shear Plate to Column Flange Weld Size
w ≥ wmin
w
11.315 mm
wmin
5 mm
Table J2.4
w ≥ wmin
w
11.315 mm
wmin
6 mm
Table J2.4
w ≥ wmin
w
11.315 mm
wmin
6 mm
Table J2.4
STRENGTH CHECKS
Flange Plate to Beam Flange Weld Strength
The nominal and design strength of the weld is checked according to AISC 360-16.
Lwı
760 mm
AISC 360-16 J2.4(c)
Lwt
210 mm
Fe
490 N/mm2
Rnwl
Rnwt
Rnw
w
11.315 mm
Fu-plate
360 N/mm2
Fu-flange
360 N/mm2
tp
16 mm
tf
17.2 mm
RnBM
Rn
ΦRn
Required
Available
Ratio
Control
505.682 kN
1140.426 kN
0.296
Flange Plate Tension Yield
The limit state of tension plate yield is checked according to AISC 360-16.
Ag
Fy
275 N/mm2
Rn
AISC 360-16 (J4-1)
ΦRn
Required
Available
Ratio
Control
505.682 kN
1108.8 kN
0.456
Flange Plate Tension Rupture
The limit state of the flange plate tension rupture is checked according to AISC 360-16.
An
Ae
Fu
410 N/mm2
U
1.00
Rn
AISC 360-16 (J4-2)
ΦRn
Required
Available
Ratio
Control
505.682 kN
1377.6 kN
0.367
Flange Plate Block Shear
The block shear limit state is checked according to AISC 360-16.
Ag
Anv
Ant
Fy
275 N/mm2
Fu
410 N/mm2
Ubs
1.0
Rn
AISC 360-16 (J4-5)
ΦRn
Required
Available
Ratio
Control
505.682 kN
2538 kN
0.199
Flange Plate Compression Yield
The limit state of compression plate yield is checked according to AISC 360-16.
K
0.65
L
20 mm
r
4.619 mm
KL / r
2.81
Fy
275 N/mm2
Ag
Rn
AISC 360-16 (J4-6)
ΦRn
Required
Available
Ratio
Control
505.682 kN
1108.8 kN
0.456
Shear Plate to Column Flange Weld Strength
w
11.315 mm
FE
490 N/mm2
l
260 mm
e
117.5 mm
Rn
ΦRn
Required
Available
Ratio
Control
135.975 kN
498.69 kN
0.273
Shear Plate to Beam Web Weld Strength
Fe
490 N/mm2
w
11.315 mm
Fu
360  N/mm2
t
11.1 mm
Rnw
RnBM
AISC Manual 14th 8-12
Rn
ΦRn
Required
Available
Ratio
Control
579.254 kN/m
1764 kN/m
0.328
Web Plate Shear Yield
The nominal and design yield strength of the web plate is checked according to AISC 360-16
Ag
Fy
275 N/mm2
Rn
AISC 360-16 J4-3
ΦRn
Required
Available
Ratio
Control
135.975 kN
429 kN
0.317
Web Plate Shear Rupture
The limit state of the web plate shear rupture is checked according to AISC 360-16.
Anv
Fu
410 N/mm2
Rn
AISC 360-16 J4-3
ΦRn
Required
Available
Ratio
Control
135.975 kN
372.69 kN
0.365
Web Plate Flexural Yield
The limit state of the web plate shear yield is checked according to AISC 360-16.
dp
260 mm
Fy
275 N/mm2
tp
10 mm
a
117.5 mm
Rn
ΦRn
Required
Available
Ratio
Control
135.975 kN
273.948 kN
0.496
Column Panel Zone Shear
The welded flange plate connection's panel zone shear limit state is checked according to AISC 360-16.
Pr
1621.397 kN
AISC 360-16 J10-9
Py
Fy
275000 kN/m2
Ag
28634.759 mm2
dc
650 mm
tw
16 mm
Rn
ΦRn
Required
Available
Ratio
Control
56.746 kN
1544.4 kN
0.037