8-Bolts Stiffened End Plate Connection Design per AISC 358-16 & AISC 360-16
How does ideCAD design eight bolts stiffened end plate connection according to AISC 358-16 & AISC 360-16?
  • Eight-bolts stiffened end plate connection is designed automatically according to the AISC 358-16 and AISC 360-16 by the ideCAD Structural.
Ag: Gross area
An: Net cross-section area
Aw: Cross-section web area
bp = width of end-plate, in. (mm)
g = horizontal distance between bolts, in. (mm)
dh: Bolt hole diameter
nsp: Number of slip planes
L: Connector distance
pb = vertical distance between the inner and outer row of bolts in an eight-bolt stiffened connection, in. (mm)
pfi = vertical distance from the inside of a beam tension flange to the nearest inside bolt row, in. (mm)
pfo = vertical distance from the outside of a beam tension flange to the nearest outside bolt row, in. (mm)
tbf = thickness of beam flange, in. (mm)
Rn: Characteristic strength
Rnt: Characteristic tensile strength
Rnv: Characteristic shear strength
Connection Geometry
GEOMETRY CHECKS
Bolts Spacing
The distance between the centers of bolts is checked per AISC 360-16.
smin ≥ 3d
AISC 360-16 J3.3
s
90 mm
d
30 mm
s =90 mm > smin = 3*30=90 mm
Horizontal Edge Distance
Leh ≥ Le-min
AISC 360-16 J3.4
Leh
70 mm
L eh ≥ 2d = 2 * 30 = 60 mm conformity check for application
Le-min
38 mm
Vertical Edge Distance
Lev ≥ Le-min
AISC 360-16 J3.4
Lev
70 mm
Leh ≥ 2d = 2 * 30 = 60 mm conformity check for application
Le-min
38 mm
Beam Web to End Plate Weld Size
w ≥ wmin
w
7.072 mm
wmin
5 mm
Table J2.4
Stiffener to Beam Flange Weld Size
w ≥ wmin
w
8.487 mm
wmin
6 mm
Table J2.4
Stiffener to End Plate Weld Size
w ≥ wmin
w
8.487 mm
wmin
6 mm
Table J2.4
w ≥ wmin
w
11.315 mm
wmin
6 mm
Table J2.4
w ≥ wmin
w
11.315 mm
wmin
6 mm
Table J2.4
PREQUALIFICATION LIMITS (TBDY Tablo 9B.1)
Beam span / Beam cross-section height
9144 mm /450 mm=20.32
≥7.0
End plate thickness, tp
30 mm
19≤tp ≤64
End plate width, bp
280 mm
229≤ bp ≤ 381
Horizontal distance between bolts, g
140 mm
127≤g≤152
pfi
50 mm
41≤pfi ≤51
pfo
50 mm
41≤pfo ≤51
pb
90
89≤pfo ≤95
Beam depth, db
450 mm
457≤db≤914
Beam flange thickness, tbf
15 mm
14≤tbf ≤25
Beam flange width, bbf
190
190≤bbf ≤311
Column depth
650
≤ 920 mm
Bolt grade
10.9
8.8 - 10.9
Min yield stress of the end plate material
275 MPa
235 /275 / 355 MPa
Flange plate weld
CJP
CJP
Strength Checks
Bolt Diameter
The required bolt diameter, db, for Eight bolts unstiffened end plate connection is checked according to AISC 358-16 §6.8
Muc
861.35 kNm
AISC 358-16 (6.8-4)
Ft
750000 kN/m2
h1
h2
h3
h4
db
Required
Available
Ratio
Control
21.607 mm
30 mm
0.720
End Plate Thickness
The required end plate thickness, tb, for eight bolts stiffened end plate connection is checked according to AISC 358-16 §6.8
Muc
861.35 kNm
AISC 358-16 (6.8-5)
Fyp
275 N/mm2
s
Yp
Yp
tp
Required
Available
Ratio
Control
23.395 mm
30 mm
0.780
End Plate Stiffener Thickness
The required stiffener thickness, tb, for eight bolts stiffened end plate connection is checked according to AISC 358-16 §6.8
tbw
9 mm
AISC 358-16 (6.8-9)
Fyb
275 N/mm2
Fys
275 N/mm2
ts
15 mm
Required
Available
Ratio
Control
9 mm
15 mm
0.600
End Plate Stiffener Local Buckling
Stiffener local buckling limit state for eight bolts stiffened end plate connection is checked according to AISC 358-16 §6.8
hs
210 mm
AISC 358-16 (6.8-10)
ts
15 mm
E
20000000 kN/m2
Fys
275000 kN/m2
Required
Available
Ratio
Control
14 mm
15.102 mm
0.927
The required end weld size for eight bolts stiffened end plate connection is checked.
Fys
275000 kN/m2
AISC DG 4-2nd
3.2.10
ts
15 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
7.938 mm
8.487 mm
0.935
Fys
275000 kN/m2
AISC DG 4-2nd
3.2.10
ts
15 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
7.938 mm
8.487 mm
0.935
Bolt Shear Rupture Check
The shear limit state of end plate bolts is checked according to AISC 360-16.
Ab
AISC 358-16 6.8-11
Fn
Rn
ΦRn
Required
Available
Ratio
Control
272.371 kN
2290.22 kN
0.119
Bolt Bearing on End Plate
Bearing strength limit states of the connection plate that are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts are checked according to AISC 360-16.
dh
30+3=33 mm
Lc,edge
Rn
AISC 358-16 6.8-12
Rn-edge
Lc,spacing1
Rn-spacing1
Lc,spacing2
Rn-spacing2
Rn
ΦRn
Required
Available
Ratio
Control
272.371 kN
6044.22 kN
0.045
Bolt Bearing on Column Flange
dh
30+3=33 mm
Rn
AISC 358-16 6.8-12
Rn-edge
Lc,spacing1
Rn-spacing1
Lc,spacing2
Rn-spacing2
Rn
ΦRn
Required
Available
Ratio
Control
272.371 kN
6424.142
0.042
The required end weld size for eight bolts stiffened end plate connection is checked according to AISC 358-16 §6.7
Fyp
275000 kN/m2
AISC 358-16
6.7.6 (3)
tbw
9 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
4.763 mm
7.072 mm
0.673
Column Flange Thickness
The required column flange thickness, tcf, for four bolts unstiffened end plate connection is checked according to AISC 358-16 §6.8
Muc
861.352 kNm
AISC 358-16 (6.8-13)
Fyp
275000 kN/m2
s
c
Yc
Yc
tcf
Required
Available
Ratio
Control
22.137 mm
31 mm
0.714
Column Panel Zone Shear
Yielding of the column panel zone for eight bolts unstiffened end plate connection is checked according to AISC 360-16 §J.10
Pr
625.405 kN
AISC 360-16 J10-9
Py
Fy
275000 kN/m2
Ag
28634.759 mm2
dc
650 mm
tw
16 mm
Rn
ΦRn
Required
Available
Ratio
Control
1754.043 kN
1716 kN
1.022
ꭓ
Panel Zone Thickness
The required panel zone thickness for eight bolts unstiffened end plate connection is checked according to AISC 358-16.
tmin≥u/180
TBDY 2018 9.3.4.2b
tmin = t w
16 mm
tw
16 mm
u
2016 mm
Required
Available
Ratio
Control
11.2 mm
16 mm
0.700