Column-Foundation Connection (Stiffened Baseplate) Design per AISC 360-16 & Design Guide 1
How does ideCAD design Column-Foundation Connection (Stiffened Baseplate) according to AISC 360-16 & Design Guide 1?
  • Limit states of Column-Foundation Connection (Stiffened Baseplate) are checked automatically according to AISC 360-16 & Design Guide 1.
  • Anchor Rod Concrete Pullout limit state is checked automatically according to ACI 319M-18.
Ag: Gross area
A1: Area of the base plate,
A2: Area of the supporting surface
d: Characteristic diameter of the stem of the bolt (the diameter of the non-threaded stem of the bolt)
dh: Bolt hole diameter
e: equivalent eccentricity
fc: Concrete design compressive strength
t: Plate thickness
w = Size of weld leg, in. (mm)
Rn: Characteristic strength
GEOMETRY CHECKS
Bolt Spacing
The distance between the centers of bolts is checked per AISC 360-16.
smin ≥ 3d
AISC 360-16 J3.3
s
180 mm
d
24 mm
s =180 mm > smin = 3*24=72 mm
Horizontal Edge Distance
Leh ≥ Le-min
AISC 360-16 J3.4
Leh
70 mm
L eh ≥ 2d = 2 * 24 = 48 mm conformity check for application
Le- min
30 mm
Vertical Edge Distance
Lev ≥ L e-min
AISC 360-16 J3.4
Lev
45 mm
Le-min
30 mm
Strength Controls
Base Plate Thickness (Compression)
The required plate thickness is determined according to AISC Steel Design Guide 1 Eq.3.3.15a.
fc
25000 kN/m2
A1
A2
qmax
fp(max)
fp(max)
e
ecrit
Y
Y
f
le
45 mm
l
max(m,n)=141.25
m
n
h
650 mm
b
300 mm
N
900 mm
B
500 mm
M
365.17 kNm
P
739.22 kN
y
355 N/mm2
treq
AISC DG-1-2nd
3.3.15.a
Required
Available
Ratio
Control
41.11 mm
42 mm
0.979
Base Plate Thickness (Tension)
The required base plate thickness for tension is determined according to AISC Steel Design Guide 1 Eq.3.4.7a.
fc
25000 kN/m2
A1
A2
qmax
e
ecrit
T
Y
Y
f
x
le
45 mm
m
h
650 mm
N
900 mm
B
500 mm
M
365.17 kNm
P
739.22 kN
Fy
355 N/mm2
treq
AISC DG-1-2nd
3.4.7a
Required
Available
Ratio
Control
15.312 mm
42 mm
0.365
Anchor Rod Tensile Rupture
The limit state of the anchor rod tension rupture is checked according to AISC 360-16.
Ab
Fn
750000 kN/m2
Rn
AISC 360-16 J3-1
ΦRn
Required
Available
Ratio
Control
28.779 kN
254.469 kN
0.113
The limit state of the anchor concrete pullout is checked according to ACI 318M-08.
Ψ
1.0
ACI 318M-08 D.5.3.6
Np
ACI 318M-08 (D-15)
Abgr
7401.592 mm2
fc
25000 kN/m2
Rn
ACI 318M-08 (D-14)
ΦRn
Required
Available
Ratio
Control
28.779 kN
1036.222 kN
0.028
Anchor Rod Shear
The calculation is made using the Elastic method, one of the methods selected in the steel analysis settings tab. In this check, the operation is performed on half of the symmetry axis and is calculated to form a force pair with the required force.
Ab
Fn
Rn
AISC 360-16 J3-1
ΦRn
Required
Available
Ratio
Control
9.885 kN
152.681 kN
0.065
Bolt Bearing on Plate
The bearing strength limit states of the base plate, which are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts, are checked according to AISC 360-16.
dh
24+3=27 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Rn
ΦRn
Required
Available
Ratio
Control
9.885 kN
559.629 kN
0.018