Architecture & Structural Engineering

Slabs With Mesh Wire

Analysis, design and code requirements check results of mesh-reinforced slabs are given in the Slabs With Mesh Wire dialog. Detail results of floors designed as mesh reinforcement are given in this dialog.

In order to see the design results in the Slabs With Mesh Wire dialog, the Use mesh wire option in the Mesh Wire tab of the Slab Settings window must be checked.

image-20240314-055437.png

The Place of Slabs With Mesh Wire Dialogue

After the analysis, you can access it by clicking the Wire Mesh Reinforced Flooring command under the ribbon menu Analysis and Design tab, Reinforced Concrete Design heading .

image-20210915-075008.png

Wire Mesh Reinforced Floor Dialogue General Features

Using the Shift key

In this tab, you can select more than one row with the Shift key, enter a value by double-clicking on any cell whose value is open to change, and make that value apply to all selected rows.

Using the Ctrl key

The Ctrl key selects the in-between lines one by one.

Show all stories

image-20210915-075045.png

When checked, it lists the tiles across the entire floor. When unchecked, only the tiles of the running active floor are listed.

Show top mesh reinforcements of selected floors

image-20210915-075103.png

For any marked slab or slabs group, it lists the rebars on top of the slabs. Otherwise, a list of all tiles is given.

OK

image-20210915-075321.png

Closes the dialog by saving the changes made.

Cancel

image-20210915-075334.png

Closes the dialog without saving the changes made.

Insufficiency Code

Description

Min

The slab does not satisfy the minimum thickness requirement according to the design code.
Recommended action: Increase the slab thickness.

Çd

The slab is acting as a doubly reinforced section, which is not permitted for slabs.
Recommended action: Increase the slab thickness.

S

The slab does not meet the deflection (serviceability) criteria according to the design code.
Recommended action: Increase the slab thickness.

As(–)

The slab has insufficient reinforcement; an adequately large bar diameter may not have been selected.
Recommended action: Select a larger-diameter bar or reduce bar spacing to achieve the required reinforcement area.


Under Meshwires:

Detailed information of the reinforcements placed in the lower part of the slab section is given.

image-20210915-075414.png


Features

DS

image-20201228-144414.png

It is the reinforcement fixing column. If marked, the reinforcement is fixed. When the mesh reinforcements are changed, the DS is marked automatically and the tooth reinforcement remains fixed when the calculation is made again.

ID

image-20210915-075727.png

It is the name of the floor that appears in the plan. (D1, D2, D10 etc.) In case of negativity, the term related to the negativity is added next to the name of the record. D101(Min) etc text appears.

Story

image-20210915-075740.png

It is the name of the floor where the flooring is located.

Meshwire

image-20210915-075749.png

It is the mat type placed under the floor section.

M1

image-20210914-125442.png

It is the highest moment value in the 1 direction of the slab, in the lower part of the slab, which is taken as a basis for the selection of the wicker reinforcement.

M2

image-20210914-125548.png

It is the highest moment value on the other side of the slab, in the lower part of the slab, which is taken as a basis for the selection of the wicker reinforcement.

Calc. As1

image-20210915-080448.png

It is the amount of reinforcement in area calculated using the M1 moment in the 1 direction.

Req. As1

image-20210915-080456.png

It is the amount of reinforcement in terms of area that should be placed in the section in the 1 direction as per the regulation.

Extra As1

image-20210915-080515.png

It is the difference of the current reinforcement amount selected for the section in the 1 direction, whichever is greater than the calculation As1 or the calculation As1 values.

Calc. As2

image-20210915-080528.png

It is the amount of reinforcement in area calculated using the M2 moment.

Req. As2

image-20210915-080708.png

It is the amount of reinforcement that should be placed in the section in accordance with the regulation in the 2 direction.

Extra As2

image-20210915-080730.png

It is the amount of excess reinforcement in the section after the selection of reinforcement in the section in the 2 direction.

Upper Meshwires:

Detailed information of the reinforcements placed in the upper part of the slab section is given.

image-20210915-075414.png

Features

Support ID

image-20210915-080810.png

The name of the support area of ​​the slab is written.

Story

image-20210915-080824.png

It is the name of the floor where the flooring is located.

Slabs

image-20210915-080831.png

The names of the slabs attached to the relevant support are given.

Meshwire

image-20210915-080853.png

It is the name of the wicker reinforcement placed in the support area.

Moment

image-20210915-080904.png

It is the design moment based on the mesh reinforcement calculation on the relevant support.

Calc.As.

image-20210915-080918.png

It is the value of the reinforcement found from the moment in terms of area.

Req.As.

image-20210915-080929.png


It is the value in terms of area of ​​the reinforcement that should be placed in the support area as per the regulation.

Extra As.

image-20210915-080949.png

It is the amount of excess reinforcement in the section after the reinforcement selection.


Next Topic