Unstiffened Seated Connection Design per AISC 360-16
How does ideCAD design unstiffened seated connection according to AISC 360-16?
  • Unstiffened seated connection limit states and geometry checks are done automatically according to AISC 360-16.
  • The block shear limit state is checked automatically according to AISC 360-16.
  • Limit states of single plate web yielding, web crippling and weld strength are checked automatically.
Connection Geometry
Geometry Checks
Weld Size
w ≥ wmin
w
11.315 mm
wmin
5 mm
Table J2.4
Strength Checks
Beam Web Yielding
The limit state of web local yielding for single-concentrated forces and both components of double-concentrated forces are checked according to AISC 360-16.
tw
7.1 mm
lb
25.7 mm
to
10.7 + 15 = 25.7 mm (Beam flange + Beam flange radius)
Fy
235.359 N/mm2
Rn
AISC 360-16 Eq. J10-3
Rn / Ω
Required
Available
Check
Result
73.288 kN
100.207 kN
0.732
Beam Web Crippling
The limit state of web local crippling for single-concentrated forces and both components of double-concentrated forces are checked according to AISC 360-16.
tw
7.1 mm
tf
10.7 mm
lb
25.7 mm
d
300 mm
E
205939650 kN/m2
Fy
235.359 N/mm2
Rn
AISC 360-16 Eq. J10-5a
Rn / Ω
Required
Available
Check
Result
73.288 kN
98.138 kN
0.747
Angle Shear Yield
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear yielding is checked according to AISC 360-16.
Ag
Fy
235.359 N/mm2
Rn
AISC 360-16 J4-3
Rn / Ω
Required
Available
Check
Result
73.288 kN
141.215 kN
0.519
Weld Strength at Support
Fe
480000 kN/m2
w
11.315 mm
Fu
362.846  N/mm2
l
110 mm
e
60mm
Rn
Rn / Ω
Required
Available
Check
Result
73.288 kN
74.06 kN
0.990