4 Bolt Unstiffened End Plate Connection Design
4 bolt unstiffened end plate connection is a moment-resisting connection (rigid connection) that is connected to the columns' flange to the beams. Bolt control, weld control, plate control and connection application limits control are performed automatically according to the placement of the elements of the connection. 4 bolt unstiffened end plate connection is made automatically according to the Design, Calculation and Construction Principles of Steel Structures (ÇYTHYEDY) or AISC 360-16 regulations and the connection report is generated. Connection detail application limits are checked according to TBDY Table 9B.1.
In the calculation of the connection, the horizontal and vertical bolt distances, end plate weld thickness, continuity plate weld thickness and application limits are checked under geometry control. In strength checks, bolt diameter, end plate thickness, end plate shear yield, end plate shear failure, etc. are checked and reported.
Connection Geometry
Geometry Checks
Horizontal Edge Distance
ÇYTHYEDY 13.3.7
70 mm
L eh ≥ 2d = 2 * 30 = 60 mm conformity check for application
40 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance
ÇYTHYEDY 13.3.7
85 mm
40 mm
Beam Web to End Plate Weld Size
6 mm
3.5 mm
Table 13.4
8 mm
4 mm
Table 13.4
8 mm
4 mm
Table 13.4
Connection Detail Prequalification Limits (TBDY Table 9B.1)
Beam span / Beam cross-section height
9144 mm /450 mm=20.32
≥7.0
End plate thickness, tp
32 mm
12≤t p ≤60
Head plate width, bp
290 mm
160≤ b p ≤ 300
Horizontal distance between bolts, g
150 mm
100≤g≤155
pfi
60 mm
40≤p fi ≤115
pfo
60 mm
40 p fo ≤115
Beam cross-section height, db
450 mm
270≤ d b ≤ 1400
Beam flange thickness, tbf
15 mm
10≤t bf ≤25
Column cross-section height
650
≤ 920 mm
Bolt class
10.9
8.8 - 10.9
Min yield stress of the end plate material
275 MPa
235 /275 / 355 MPa
Flange plate welding
CJP
CJP
Strength Checks
Bolt diameter
783.345 kNm
AISC 358-16 (6.8-3)
750000 kN/m2
x1
Required
Ready
Ratio
Control
29.141 mm
30 mm
0.971
End Plate Thickness
783.345 kNm
AISC 358-16 (6.8-5)
275000 kN/m2
s
Yp
Yp
tp
Required
Available
Ratio
Control
30.74 mm
32 mm
0.961
End Plate Shear Yield
783.345 kNm
AISC 358-16 (6.8-7)
275000 kN/m2
290 mm
32 mm
d
450 mm
15 mm
Required
Available
Ratio
Control
900,396 kN
1531.2 kN
0.588
End Plate Shear Rupture
783.345 kNm
AISC 358-16 (6.8-7)
Fup
410000 kN/m2
d
450 mm
15 mm
Required
Available
Ratio
Control
900,396 kN
1027.3 kN
0.876
Bolt Shear at Support
Required
Available
Ratio
Control
212.57 kN
1145.11 kN
0.186
Bolt Bearing on End Plate
30+3=33 mm
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Required
Available
Ratio
Control
212.57 kN
3400.704 kN
0.063
Bolt Bearing on Column Flange
30+3=33 mm
ÇYTHYEDY 13.3.13
Required
Available
Ratio
Control
212.57 kN
3294.432 kN
0.065
Beam Web to End Plate Weld Strength
275000 kN/m2
AISC 358-16
(6.7.6) 3
9 mm
490000 kN/m2
w
Required
Available
Ratio
Control
4.763 mm
8.487 mm
0.561
Column Flange Thickness
783.345 kNm
AISC 358-16 (6.8-5)
275000 kN/m2
s
c
Yc
Yc
Required
Available
Ratio
Control
24.324 mm
31 mm
0.785
Column Panel Zone Shear
429.124 kN
ÇYTHYEDY 13.29a
275000 kN/m2
28634.759 mm2
650 mm
16 mm
Required
Ready
Ratio
Control
1595.191 kN
1716 kN
0.930
Panel Zone Thickness
tmin ≥u / 180
TBDY 2018 9.3.4.2b
tmin = tw
16 mm
16 mm
u
2016 mm
Required
Available
Ratio
Control
11.2 mm
16 mm
0.700