Single Angle Connection
A single angle connection is a type of connection that connects two profiles to each other with one angle bracket (cornier or L profile). Bolt control, weld control and plate control are performed automatically according to the placement of the elements of the connection. Single angle connection design is made automatically according to the Design, Calculation and Construction Principles of Steel Structures (ÇYTHYEDY) (GKT and YDKT) or AISC 360-16 (ASD and LRFD) regulations and the connection report is created.
In the calculation of the connection with single angle plate, the distance control between the bolts, horizontal and vertical edge distance control, weld thickness control, mounting stability controls are made as geometry control. Angle shear yielding, beam and angle shear failure, block slip in beam and angle iron, crushing in beam and angle bolt holes, shear in beam bolts, welding strength are checked as strength control.
Connection Geometry
Geometry Checks
Bolt Spacing
ÇYTHYEDY 13.3.6
79.5 mm
20 mm
s =79.5 mm > smin = 3*20=60 mm
Horizontal Edge Distance
ÇYTHYEDY 13.3.7
50.75 mm
L eh ≥ 2d = 2 * 20 = 40 mm conformity check for application
26 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance
ÇYTHYEDY 13.3.7
40 mm
26 mm
Weld Thickness
ÇYTHYEDY 13.3.7
6 mm
3.5 mm
Table 13.4
Erection Stability
ÇYTHYEDY 13.3.7
L
239 mm
248.6 mm
L=239 > 248.6/2=124.3 mm
Strength Checks
Angle Shear Yield
235.359 N/mm2
ÇYTHYEDY 13.17
Required
Available
Ratio
Control
93.805 kN
270 kN
0.347
Beam Shear Rupture
362.846 N/mm2
ÇYTHYEDY 13.18
Required
Available
Ratio
Control
93.805 kN
176.213 kN
0.532
Angle Shear Rupture at Beam
362.846 N/mm2
ÇYTHYEDY 13.18
Required
Available
Ratio
Control
93.805 kN
218.143 kN
0.43
Angle Block Shear at Beam
235.359 N/mm2
362.846 N/mm2
one
ÇYTHYEDY 13.19
Required
Available
Ratio
Control
93.805 kN
252,971 kN
0.371
Bolt Bearing on Beam
20+2=22 mm
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Required
Available
Ratio
Control
93.805 kN
185,487 kN
0.506
Bolt Bearing on Angle at Beam
20+2=22 mm
ÇYTHYEDY 13.3.13
Required
Available
Ratio
Control
93.805 kN
284.75 kN
0.329
Bolt Shear at Beam
Required
Available
Ratio
Control
51.448 kN
56,549 kN
0.910
Weld Strength at Support
480000 kN/m2
in
The weld thickness taken from the combination menu is 0.707 * w value. 6 / 0.707 = 8.487 mm
362.846  N/mm2
t
12 mm
Required
Available
Ratio
Control
342.216 kN/m
864 kN/m
0.396