Column shear safety check of the 3rd floor S07 column:
Major and minor bending moments and beam bearing strength moments can be seen at the upper and lower joints in the column reinforced concrete dialogue.
Major 3 direction: Mra + Mrü = 37.874 tfm> 1.2 (Mri + Mrj) = 6.889 tfm is provided.
In the direction of minor 2: Mra + Mrü = 17.608 tfm> 1.2 (Mri + Mrj) = 13.624 tfm is provided.
Major 3 axis:
M = 8.002 * 2.519 / (2.519 + 2.563) = 3.97 tfm
Ma = 8.002 * 0.677 / (0.677 + 0.956) = 3.32 tfm
Ln = floor height- beam height = 2.80- 0.50 = 2.30 m
And = (3.97 + 3.32) / 2.30
And = 3.17 tf
Minor 2 axis:
M = 15.894 * 2.15 / (2.15 + 2.26) = 7.75 tfm
Ma = 15.894 * 0.451 / (0.451 + 0.524) = 7.35 tfm
And = (7.75 + 7.35) / 2.30
And = 6.56 tf
The sum of the shear force calculated from the earthquake increased with D with the vertical loads, Eq. If calculated by (7.5) is less than Ve, this shear force will be used instead of Ve. The upper bound value for ve is given in column V in the report.
Ve = 3.17 tf <V = 5.84 (used Ve = 3.17 tf)
Ve = 6.56 tf> V = 5.79 (used Ve = 5.97 tf)
And <0.85 root (fck) * Aw fcd
and
And <Vr
should be.
Major Vr account
Vc = 0 (TBDY Article 7.3.7.6 is not provided)
Vw = (As * Coefficient / range) * fywd * b
Vw = (0.5cm * 3 / 8 cm) * 1/100 * 37241.81tf/m2 * 0.575m=40.15 tf
Vr = Vc + Vw = 0 + 40.15
Vr = 40.15 tf
And = 3.17 tf <Vr = 40.15 provided
And = 3.17 tf <0.85 Ack root (fck) = 0.85 * 300 * 600 * root (30) = 838015.513 KN = 85.45 tf provided
Minor Vr account
Vw = (0.5cm * 5 / 8 cm) * 1/100 * 37241.81tf/m2 * 0.275 m=32 tf
Vr = Vc + Vw
Vr = 0 + 32
Vr=32 tf
And = 5.97 tf <Vr = 40.15 provided
And = 5.97 tf <0.85 A root (fck) = 0.85 * 300 * 600 * root (30) = 838015.513 KN = 85.45 tf provided