T-Plate Connection Design per AISC 360-16
How does ideCAD design T-plate connection according to AISC 360-16?
  • T-plate connection limit states and geometry checks are done automatically according to AISC 360-16.
  • The block shear limit state is checked automatically according to AISC 360-16.
  • Limit states of single plate flexural yield, plate flexural bucking, and weld strength are checked automatically.
Ag: Gross area
An: Net cross-section area
Aw: Cross-section web area
Cv: Coefficient of reduction for shear buckling
d: Characteristic diameter of the stem of the bolt (the diameter of the non-threaded stem of the bolt)
dh: Bolt hole diameter
nsp: Number of slip planes
L: Connector distance
t: Plate thickness
Rn: Characteristic strength
Rnt: Characteristic tensile strength
Rnv: Characteristic shear strength
Ubs: A coefficient considering the spread of tensile stresses
Connection Geometry
Geometry Checks
Bolt Spacing
The distance between the centers of bolts is checked per AISC 360-16.
smin ≥ 3d
AISC 360-16 J3.3
s
80.4 mm
d
20 mm
s =80.4 mm > smin = 3*20=60 mm
Horizontal Edge Distance
Leh ≥ Le-min
AISC 360-16 J3.4
Leh
40 mm
Leh ≥ 2d = 2 * 20 = 40 mm conformity check for application
Le-min
26 mm
Vertical Edge Distance
Lev ≥ Le-min
AISC 360-16 J3.4
Lev
40 mm
Le-min
26 mm
Weld Size
a ≥ amin
a
12.73 mm
amin
5 mm
Table J2.4
Erection Stability
L ≥ hb /  2
L
160.4 mm
hb
190.4 mm
L=160.4 > 190.4/2=95.2 mm
Strength Checks
Bolt Shear at Beam
The calculation is made using the Elastic method, one of the methods selected in the steel analysis settings tab. For the details of this check, AISC Manual 14th 7-8 is used as a reference.
In this check, the operation is performed on half of the symmetry axis and is calculated to form a force pair with the required force.
Ag
Fy
235.359 N/mm2
Fn
Rn
Rn / Ω
Required
Available
Check
Result
3.67 kN
56,549 kN
0.065
Bolt Bearing on Beam
The bearing strength limit states of the plate, which are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts, are checked according to AISC 360-16.
dh
20+2=22 mm
t
6.2 mm
Lc,spacing
Rn
AISC 360-16 J3.6a
Rn-spacing
Rn
Rn / Ω
Required
Available
Check
Result
24.138 kN
107.983 kN
0.224
Bolt Bearing on Plate
Bearing strength limit states of the connection plate that are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts are checked according to AISC 360-16.
dh
20+2=22 mm
t
12 mm
Lc,edge
Rn
AISC 360-16 J3.6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
Rn / Ω
Required
Available
Check
Result
24.138 kN
180.26 kN
0.134
Beam Shear Rupture
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear rupture is checked according to AISC 360-16.
Anv
Fu
362.846 N/mm2
Rn
AISC 360-16 J4-4
Rn / Ω
Required
Available
Check
Result
24.138 kN
129.58 kN
0.186
Plate Shear Yield
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear yielding is checked according to AISC 360-16.
Ag
Fy
235.359 N/mm2
Rn
AISC 360-16 J4-3
Rn / Ω
Required
Available
Check
Result
24.138 kN
181.208 kN
0.133
Plate Shear Rupture
Anv
Fu
362.846 N/mm2
Rn
AISC 360-16 J4-4
Rn / Ω
Required
Available
Check
Result
24.138 kN
146,822 kN
0.164
Plate Block Shear Rupture
The block shear limit state is checked according to AISC 360-16. All block shear modes combined with tensile failure on one plane and shear failure on a perpendicular plane are checked according to AISC 360-16.
Ag
Anv
Ant
Fy
235.359 N/mm2
Fu
362.846 N/mm2
Ubs
1.0
Rn
AISC 360-16 J4-5
Rn / Ω
Required
Available
Check
Result
24.138 kN
162,972 kN
0.148
Plate Flexural Buckling
Single plate material slenderness check.
Fy
235.359 N/mm2
t
12 mm
a
113 mm
L
279 mm
λ
Required
Available
Check
≤0.70
0.29
Plate Flexural Yield
Single plate material flexural yielding check.
dp
278.6 mm
F y
235.359 N/mm2
t p
12 mm
a
112.95 mm
Rn
Rn / Ω
Required
Available
Check
Result
24.138 kN
213.295 kN
0.113
Weld Strength at Support
Fe
480000 kN/m2
w
12.73 mm
Fu
362.846  N/mm2
t
12 mm
Rnw
RnBM
Rn
Rn / Ω
Required
Available
Check
Result
0.015 kN/m
1306.245 kN/m
1.15 * 10 (-5)