Structural Systems in the Same Direction per ASCE 7-16 with ideCAD
How ideCAD defines structural systems in the same direction according to ASCE 7-16?
  • The most stringent applicable structural system limitations contained in Table 12.2-1 are applied by users.
  • The values for R, Ω0, and Cd at structural systems in Table 12.2-1 are chosen for structural steel and reinforced concrete systems by the user.
SYMBOLS
Cd = Deflection amplification factor
Ωo = Overstrength factor
12.2.3 Combinations of Framing Systems in the Same Direction
If different seismic force-resisting systems are used in combination in the same direction, the most stringent applicable structural system limitations contained in Table 12.2-1 are applied.
The intent of the provision requiring the use of the most stringent seismic design parameters (R, Ω0, and Cd) is to prevent mixed seismic force-resisting systems that could concentrate inelastic behavior in the lower stories.
12.2.3.3 R, Cd, and Ω0 Values for Horizontal Combinations
The value of the response modification coefficient, R, used for design in the direction under consideration is not greater than the least value of R for any of the systems used in that direction. The deflection amplification factor, Cd, and the overstrength factor, Ω0, is consistent with the R required in that direction.
Structural System Type
Response Modification Coefficient, R
Overstrengh Factor, Ωo
Deflection Amplification Factor, Cd
Structural System Limitations Including Structural Height, hn (ft) Limits
Seismic Design Category
B
C
D
E
F
A. Bearing Wall Systems
A1 - Special reinforced concrete shear walls
5
21/2
5
NL
NL
160
160
100
A2 - Ordinary reinforced concrete shear walls
4
21/2
4
NL
NL
NP
NP
NP
A3 - Detailed plain concrete shear walls
2
21/2
2
NL
NP
NP
NP
NP
A4 - Ordinary plain concrete shear walls
11/2
21/2
11/2
NL
NP
NP
NP
NP
B. Building Frame Systems
B1 - Steel eccentrically braced frames
8
2
4
NL
NL
160
160
100
B2 - Steel special concentrically braced frames
6
2
5
NL
NL
160
160
100
B3 - Steel ordinary concentrically braced frames
31/4
2
31/4
NL
NL
35
35
NP
B4 - Special reinforced concrete shear walls
6
21/2
5
NL
NL
160
160
100
B5 - Ordinary reinforced concrete shear walls
5
21/2
41/2
NL
NL
NP
NP
NP
B6 - Detailed plain concrete shear walls
2
21/2
2
NL
NP
NP
NP
NP
B7 - Ordinary plain concrete shear walls
11/2
21/2
11/2
NL
NP
NP
NP
NP
C. Moment-Resisting Frame Systems
C1 - Steel special moment frames
8
3
51/2
NL
NL
NL
NL
NL
C2 - Steel special truss moment frames
7
3
51/2
NL
NL
160
100
NP
C3 - Steel intermediate moment frames
41/2
3
4
NL
NL
35
NP
NP
C4 - Steel ordinary moment frames
31/2
3
3
NL
NL
NP
NP
NP
C5 - Special reinforced concrete moment frames
8
3
51/2
NL
NL
NL
NL
NL
C6 - Intermediate reinforced concrete moment frames
5
3
41/2
NL
NL
NP
NP
NP
C7 - Ordinary reinforced concrete moment frames
3
3
21/2
NL
NP
NP
NP
NP
D. Dual Systems with Special Moment Frames Capable of Resisting at Least 25% of Prescribed Seismic Foces
D1 - Steel eccentrically braced frames
8
21/2
4
NL
NL
NL
NL
NL
D2 - Steel special concentrically braced frames
7
21/2
51/2
NL
NL
NL
NL
NL
D3 - Special reinforced concrete shear walls
7
21/2
51/2
NL
NL
NL
NL
NL
D4 - Ordinary reinforced concrete shear walls
6
21/2
5
NL
NL
NP
NP
NP
E. Dual Systems with Intermediate Moment Frames Capable of Resisting at Least 25% of Prescribed Seismic Foces
E1 - Steel special concentrically braced frames
6
21/2
5
NL
NL
35
NP
NP
E2 - Special reinforced concrete shear walls
61/2
21/2
5
NL
NL
160
100
100
E8 - Ordinary reinforced concrete shear walls
51/2
21/2
41/2
NL
NL
NP
NP
NP
F. Shear Wall-Frame Interactive System with Ordinary Reinforced Concrete Moment Frames And Ordinary Reinforced Concrete Shear Walls
F1 - Shear wall-frame interactive system
41/2
21/2
4
NL
NP
NP
NP
NP
G. Cantilevered Column Systems Detailed to Conform to the Requirement for
G1 - Steel special cantilever column systems
21/2
11/4
21/2
35
35
35
35
35
G2 - Steel ordinary cantilever column systems
11/4
11/4
11/4
35
35
NP
NP
NP
G3 - Special reinforced concrete moment frames
21/2
11/4
21/2
35
35
35
35
35
G4 - Intermediate reinforced concrete moment frames
11/2
11/4
11/2
35
35
NP
NP
NP
G5 - Ordinary reinforced concrete moment frames
1
11/4
1
35
NP
NP
NP
NP
H. Steel Systems not Specifically Detailed for Seismic Resistance, Excluding Cantilever Column Systems
H - Steel Systems not Specifically Detailed for Seismic Resistance
3
3
3
NL
NL
NP
NP
NP