Single Angle Connection Design per AISC 360-16
How does ideCAD design single angle connection according to AISC 360-16?
  • Single angle connection limit states and geometry checks are done automatically according to AISC 360-16.
  • The block shear limit state is checked automatically according to AISC 360-16.
  • Limit state checks are made automatically according to AISC 360-16, depending on whether the connection type selected by the user is bolted or welded.
Ag: Gross area
An: Net cross-section area
Aw: Cross-section web area
Cv: Coefficient of reduction for shear buckling
d: Characteristic diameter of the stem of the bolt (the diameter of the non-threaded stem of the bolt)
dh: Bolt hole diameter
nsp: Number of slip planes
L: Connector distance
t: Plate thickness
Rn: Characteristic strength
Rnt: Characteristic tensile strength
Rnv: Characteristic shear strength
Ubs: A coefficient considering the spread of tensile stresses
Connection Geometry
Geometry Checks
Bolt Spacing
The distance between the centers of bolts is checked per AISC 360-16.
smin ≥ 3d
AISC 360-16 J3.3
s
79.5 mm
d
20 mm
s =79.5 mm > smin = 3*20=60 mm
Horizontal Edge Distance
Leh ≥ Le-min
AISC 360-16 J3.4
Leh
50.75 mm
Leh ≥ 2d = 2 * 20 = 40 mm conformity check for application
Le-min
26 mm
Vertical Edge Distance
Lev ≥ Le-min
AISC 360-16 J3.4
Lev
40 mm
Le- min
26 mm
Weld Size
a ≥ amin
a
6 mm
amin
3.5 mm
Table J2.4
Erection Stability
L ≥ hb /  2
L
239 mm
hb
248.6 mm
L=239 > 248.6/2=124.3 mm
Strength Checks
Angle Shear Yield
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear yielding is checked according to AISC 360-16.
Ag
Fy
235.359 N/mm2
Rn
AISC 360-16 J4-3
Rn / Ω
Required
Available
Check
Result
68,159 kN
270 kN
0.252
Beam Shear Rupture
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear rupture is checked according to AISC 360-16.
Anv
Fu
362.846 N/mm2
Rn
AISC 360-16 J4-4
Rn / Ω
Required
Available
Check
Result
68,159 kN
176.213 kN
0.387
Angle Shear Rupture at Beam
Anv
Fu
362.846 N/mm2
Rn
AISC 360-16 J4-4
Rn / Ω
Required
Available
Check
Result
68.159 kN
218.143 kN
0.312
Angle Block Shear at Beam
The block shear limit state is checked according to AISC 360-16. All block shear modes combined with tensile failure on one plane and shear failure on a perpendicular plane are checked according to AISC 360-16.
Ag
Anv
Ant
Fy
235.359 N/mm2
Fu
362.846 N/mm2
Ubs
1.0
Rn
AISC 360-16 J4-5
Rn / Ω
Required
Available
Check
Result
68.159 kN
252,971 kN
0.269
Bolt Bearing on Beam
Bearing strength limit states of the connection plate that are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts are checked according to AISC 360-16.
dh
20+2=22 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
Rn / Ω
Required
Available
Check
Result
68.159 kN
185.487 kN
0.367
Bolt Bearing on Angle at Beam
dh
20+2=22 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
Rn / Ω
Required
Available
Check
Result
68.159 kN
284.75 kN
0.239
Bolt Shear at Beam
The calculation is made using the Elastic method, one of the methods selected in the steel analysis settings tab. For the details of this check, AISC Manual 14th 7-8 is used as a reference.
In this check, the operation is performed on half of the symmetry axis and is calculated to form a force pair with the required force.
Ab
Fn
Rn
Rn / Ω
Required
Available
Check
Result
37.382 kN
56.549 kN
0.661
Weld Strength at Support
Fe
480 N/mm2
w
The weld thickness taken from the combination menu is 0.707 * w value. 6 / 0.707 = 8.487 mm
Fu
362.846  N/mm2
t
12 mm
Rnw
RnBM
Rn
R n / Ω
Required
Available
Check
Result
248.654 kN/m
864 kN/m
0.288