Calculation of Time-Dependent Deflections per ACI 318-19 with ideCAD
How does ideCAD calculate time-dependent deflections according to ACI 318-19?
  • Time-Dependent Deflection is calculated automatically.
:check_mark:
Notation
As' = area of the compression reinforcement, in2
b = width of compression face of member, in.
ρ' = ratio of As' to bd
ξ = time-dependent factor for sustained load
λΔ = multiplier used for additional deflection due to long-term effects
According to ACI 24.2.4.1.1, additional time-dependent deflection resulting from creep and shrinkage of flexural members can be calculated as the product of the immediate deflection caused by sustained load and the factor λΔ.
ρ' is the ratio of the As' , area of the compression reinforcement, to bd
Time-dependent factor ξ is 2.0 in accordance with ACI Table 24.2.4.1.3
Sustained load duration, months
Time-dependent factor, ξ
3
1.0
6
1.2
12
1.4
60 or more
2.0
:check_mark: