4 Bolts Stiffened End Plate Connection Design
The 4 Bolts Stiffened End Plate Connection is a type of moment-transmitting connection (rigid connection) which is bolted to the columns and welded to the beam and is a stiffening plate. Bolt control, weld control, plate control and connection application limits control are performed automatically according to the placement of the elements of the connection. The 4 Bolts Stiffened End Plate Connection Design is made automatically according to the Design, Calculation and Construction Principles of Steel Structures (ÇYTHYEDY) or AISC 360-16 regulations and the connection report is created. Connection detail application limits are checked according to TBDY Table 9B.1.
In the calculation of the 4 Bolts Stiffened End Plate Connection, the horizontal and vertical bolt distances, end plate weld thickness, continuity plate weld thickness and application limits are checked under geometry control. In strength checks, bolt diameter, end plate thickness, end plate shear yield, end plate shear failure, reinforcement plate weld thickness, slip on support bolts, bolt hole crush on end plate, bolt hole crush on column head, butt plate weld thickness, column head thickness, column panel zone slip and slip zone thickness control.
Connection Geometry
Geometry Checks
Horizontal Edge Distance
Leh ≥ Le- min
ÇYTHYEDY 13.3.7
Leh
72 mm
L eh ≥ 2d = 2 * 30 = 60 mm conformity check for application
Le- min
48 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance
Lev ≥ Le- min
ÇYTHYEDY 13.3.7
Lev
72 mm
Le- min
48 mm
Beam Web to End Plate Weld Size
a ≥ amin
a
5 mm
amin
3.5 mm
Table 13.4
Stiffener to Beam Flange Weld Size
a ≥ amin
a
5 mm
amin
3.5 mm
Table 13.4
Stiffener to End Plate Weld Size
a ≥ amin
a
5 mm
amin
3.5 mm
Table 13.4
a ≥ amin
a
8 mm
amin
4 mm
Table 13.4
a ≥ amin
a
8 mm
amin
4 mm
Table 13.4
Connection Detail Prequalification Limits (TBDY Table 9B.1)
Beam span / Beam cross-section height
9144 mm /450 mm=20.32
≥7.0
End plate thickness, tp
30 mm
12≤t p ≤40
Flange plate width, bp
298 mm
160≤ b p ≤ 300
Horizontal distance between bolts, g
154 mm
100≤g≤155
pfi
72 mm
45≤p fi ≤140
pfo
72 mm
45 p fo ≤145
Beam cross-section height, db
450 mm
270≤ d b ≤ 610
Beam flange thickness, tbf
15 mm
10≤t bf ≤25
Column cross-section height
650
≤ 920 mm
Bolt class
10.9
8.8 - 10.9
Min yield stress of the End plate material
275 MPa
235 /275/355 MPa
Flange plate weld
CJP
CJP
Strength Checks
Bolt diameter
Muc
803.836 kNm
AISC 358-16 (6.8-3)
Ft
750000 kN/m2
ho
h1
db
Required
Available
Ratio
Control
29.52 mm
36 mm
0.820
End Plate Thickness
Muc
803.836 kNm
AISC 358-16 (6.8-5)
Fyp
275000 kN/m2
s
Yp
Yp
tp
Required
Available
Ratio
Control
27.027 mm
30 mm
0.901
End Plate Stiffener Thickness
tbw
9 mm
AISC 358-16 (6.8-9)
Fyb
275000 kN/m2
Fys
275000 kN/m2
ts
12 mm
Required
Available
Ratio
Control
9 mm
12 mm
0.750
End Plate Stiffener Local Buckling
hs
144 mm
AISC 358-16 (6.8-10)
ts
12 mm
E
205939650 kN/m2
Fys
275000 kN/m2
Required
Available
Rate
Control
12
15.325
0.783
Fys
275000 kN/m2
AISC DG 4-2 nd
3.2.10
ts
12 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
6.35
7.072
0.898
Fys
275000 kN/m2
AISC DG 4-2 nd
3.2.10
ts
12 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
6.35
7.072
0.898
Bolt Shear at Support
Ab
Fn
Rn
ΦRn
Required
Available
Ratio
Control
214.84 kN
1648.959 kN
0.130
Bolt Bearing on End Plate
dh
36+3=39 mm
Lc,edge
Rn
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
214.84 kN
3307.716 kN
0.065
Bolt Bearing on Column Flange
db
36 mm
Rn
ÇYTHYEDY 13.3.13
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
214.84 kN
3953.318 kN
0.054
Fyp
275000 kN/m2
AISC 358-16
(6.7.6) 3
tbw
9 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
4.763 mm
7.072 mm
0.673
Column Flange Thickness
Muc
803.836 kNm
AISC 358-16 (6.8-13)
Fyp
275000 kN/m2
s
c
Yc
Yc
tcf
Required
Available
Ratio
Control
25.336 mm
31 mm
0.817
Column Panel Zone Shear
P r
429,124 kN
ÇYTHYEDY 13.29a
Py
F y
275000 kN/m2
A g
28634.759 mm2
d c
650 mm
tw
16 mm
Rn
ΦRn
Required
Available
Ratio
Control
1636.918 kN
1716 kN
0.954
Panel Zone Thickness
tmin ≥u / 180
TBDY 2018 9.3.4.2b
tmin = t w
16 mm
tw
16 mm
u
2016 mm
Required
Available
Ratio
Control
11.2 mm
16 mm
0.700