How does ideCAD control shear wall reinforcement detailing according to ACI 318-19?
Reinforcement detailing is applied automatically in accordance with ACI 11.7.
Covers of reinforced concrete elements are defined by user.
Notation
db = Nominal diameter of bar, wire, or prestressing strand, in.
Ktr = transverse reinforcement index, in.
ψe = factor used to modify development length based on reinforcement coating
ψg = factor used to modify development length based on grade of reinforcement
ψs = factor used to modify development length based on reinforcement size
ψt = factor used to modify development length for casting location in tension
Concrete cover for reinforcement should be in accordance with ACI Table 20.5.1.3.1. The concrete cover is measured to the outer edge of ties, stirrups, or spirals if transverse reinforcement encloses the main bars.
Concrete exposure |
Member |
Reinforcement |
Specified cover, in. |
Cast against and permanently in contact with ground |
All |
All |
3 |
Exposed to weather or in contact with ground |
All |
#6 through #18 bars |
2 |
#5 bar and smaller |
1-1/2 |
Not exposed to weather or in contact with ground |
Slabs, joints, and walls |
#14 and #18 bars |
1-1/2 |
#11 bar and smaller |
3/4 |
Beams, colums, pedestals |
Primary reinforcement, stirrups, ties, spirals and hoops |
1-1/2 |
Cover or specified concrete is defined as the distance between the outermost surface of embedded reinforcement and the closest outer surface of the concrete.
Development lengths of concrete beam reinforcement should be in accordance with Development of Reinforcement title. In this case, for deformed bars or deformed wires, ld is calculated in accordance with ACI Table 25.4.2.3. Other conditions are described in the same title.
Splices of deformed reinforcement should be in accordance with Splices title.