Joining Plates Design per AISC 360-16
How does ideCAD design joining plate connection according to AISC 360-16?
  • Joining plate connection limit states and geometry checks are done automatically according to AISC 360-16.
Ag: Gross area
An: Net cross-section area
d: Characteristic diameter of the stem of the bolt (the diameter of the non-threaded stem of the bolt)
dh: Bolt hole diameter
tp: Plate thickness
Pt: Bolt tensile strength
Rn: Characteristic strength
w: Size of weld leg, in. (mm)
Connection Geometry
GEOMETRY CHECKS
Horizontal Edge Distance
Leh ≥ Le-min
AISC 360-16 J3.4
Leh
55 mm
Leh ≥ 2d = 2 * 24 = 48 mm conformity check for application
Le- min
30 mm
Vertical Edge Distance
Lev ≥ Le-min
AISC 360-16 J3.4
Lev
51.519 mm
L eh ≥ 2d = 2 * 24 = 48 mm conformity check for application
Le-min
32 mm
Weld Size
w ≥ wmin
AISC 360-16 J2.4
w
8.487 mm
wmin
5 mm
Table J2.4
STRENGTH CHECKS
Bolt Tension at Support
Bolt tensile strength is checked due to axial force and bending moment interaction effect.
Ft
750000 kN/m2
Ab
AISC DG-4-2nd
3.7
Pt
h0
473.038 mm
h1
315.271 mm
dm
394.154 mm
Mreq
119.655 kNm
Nreq
-27.504 kN
Rreq
Rn
ΦRn
Required
Available
Ratio
Control
289.822 kN
1017.876 kN
0.285
End Plate Thickness
The required end plate thickness, tp, for four bolts stiffened end plate connection is checked according to AISC 358-16 §6.8
Ab
Pt
Mn
AISC 358-16 (6.8-5)
Fyp
235000 kN/m2
Yp
2517.347 mm
tp
Required
Available
Ratio
Control
28.921 mm
30 mm
0.964
End Plate Shear Yield
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear yielding is checked according to AISC 360-16.
Fyp
235000 kN/m2
Ag
AISC 360-16 J4-3
dm
394.154 mm
Mreq
119.655 kNm
Nreq
-27.504 kN
Rreq
Rn
ΦRn
Required
Available
Ratio
Control
289.822 kN
1776.6 kN
0.163
End Plate Shear Rupture
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear rupture is checked according to AISC 360-16.
Fu
360000 kN/m2
An
AISC 360-16 J4-4
dm
394.154 mm
Mreq
119.655 kNm
Nreq
-27.504 kN
Rreq
Rn
ΦRn
Required
Available
Ratio
Control
289.822 kN
1477.44 kN
0.196
Bolt Shear at Support
The calculation is made using the Elastic method, one of the methods selected in the steel analysis settings tab. For the details of this check, AISC Manual 14th 7-8 is used as a reference. In this check, the operation is performed on half of the symmetry axis and is calculated to form a force pair with the required force.
Ab
Fnv
Rn
AISC 360-16 J3-1
ΦRn
Required
Available
Ratio
Control
5.313 kN
610,725 kN
0.009
Bolt Bearing on End Plate
Bearing strength limit states of the connection plate that are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts are checked according to AISC 360-16.
dh
24+3=27 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
5.313 kN
1672.2kN
0.003
Weld Size
The required end weld size is checked according to AISC DG-4.
Fyp
235000 kN/m2
AISC DG-4-2 nd
2.1.7
tbw
9 mm
Fe
480000 kN/m2
w
Required
Available
Ratio
Control
3.97 mm
8.487 mm
0.468
Weld Strength
The required end weld strength is checked according to AISC DG-4.
w
8.487 mm
FE
480 N/mm2
le
190.193 mm
Rn
AISC DG-4-2 nd
2.1.8
ΦRn
Required
Available
Ratio
Control
5.313 kN
492.981 kN
0.011