Architecture & Structural Engineering

Steel Column Design Example

How do you design a steel column with ideCAD?

Steel Column Design strength control of the steel column named PL007 is done under the most unfavorable internal forces due to the general analysis determined according to International Steel Design Codes. The material and section information of the column are as follows:

Steel material: S355 Fy =355 N/mm 2 Fu =510 N/mm 2

Cross section: HEB 450

Ix = 79890 cm4

Iy = 11720 cm4

Jx = 440.5 cm4

Cw = 5258000 cm6

Wex = 3551 cm3

Wpx = 3982 cm3

A= 218 cm4


d=450 mm

h=344 mm

bf = 300 mm

tf = 26 mm

tw = 14 mm

ix=191.4 mm

iy=73.3 mm


Control of Cross-Section Conditions (TBDY 9.3.1)

It should be checked whether the flange width/thickness and web height/thickness values ​​of the column cross-section exceed λhd value given in Table 9.3 .

  • Cross-section flange;

koşulu sağlar.

  • Cross-section web;

As a result of the analysis, the column design point is taken from the cross-section.

koşulu sağlar.

Check of the cross-section condition is made according to the TBDY 2018 Table 9.3 in the steel column report and summarized in tabular form.

d3.png

Axial Force Strength

The calculation of the flexural buckling boundary state about the X-axis is as follows:

MPa

MPa

The calculation of the flexural buckling boundary state about the Y-axis is as follows:

MPa

MPa

kN

Flexural Moment Strength

mm

mm

Since Lr is calculated.

48.png

In this case, the characteristic bending moment strength should be calculated by ÇYTHYE Equation 9.3. Cb, the lateral-torsional buckling modification factor, used in this calculation is determined automatically according to the moment values ​​read on the relevant column.

50.png
49.png

According to design rules under combined effects, strength control is done as follows:

51.png

Shear Force Strength

According to section 10.2.1(a) of ÇYTHYE in I-cross section with double symmetry axes,

52.png

According to ÇYTHYE 10.2,

53.png

Axial Capacity Control

In addition to the axial capacity we design the elements under combined effects above, the axial tensile force must also be controlled in accordance with TBDY 9.3.1.3. The point to be considered in this check is that the horizontal earthquake effects obtained from the analysis must be increased by D, overstrenght factor.

d4.png