Single Plate Connection
A single plate connection is a non-moment transfer connection (hear connection) that is bolted to the body of the profile and welded to the support. Bolt control, weld control and plate control are performed automatically according to the placement of the elements of the connection. Connection design with single plate is made automatically according to the Design AISC 360-16 (ASD and LRFD) regulations and the connection report is generated.
In the connection calculation with single plate, distance control between bolts, horizontal and vertical edge distance control, weld thickness control, mounting stability controls are made as geometry control. As a strength control, checks are made for shear in beam bolts, crushing in beam and plate bolt holes, plate shear yielding, beam and plate shear failure, plate block slip, plate bending buckling, plate bending yield, support welding strength.
:check_mark:
Download ideCAD for Connection Design with AISC 360-16
Get Started FREE Software for Steel Connections
Connection Geometry
Geometry Checks
Spacing between bolts
ÇYTHYEDY 13.3.6
79.5 mm
20 mm
s =79.5 mm > smin = 3*20=60 mm
Horizontal Edge Distance
ÇYTHYEDY 13.3.7
40 mm
L eh ≥ 2d = 2 * 20 = 40 mm conformity check for application
26 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance
ÇYTHYEDY 13.3.7
40 mm
26 mm
Weld Thickness
ÇYTHYEDY 13.3.7
9 mm
3.5 mm
Table 13.4
Erection Stability
ÇYTHYEDY 13.3.7
L
239 mm
248.6 mm
L=239 > 248.6/2=124.3 mm
Strength Checks
Bolt Shear at Beam
  • Calculation is made using Elastic method, one of the methods selected in the steel analysis settings tab. For the details of this calculation, AISC Manual 14th 7-8 is used as a reference.
  • In this calculation, the operation is performed on half of the symmetry axis and it is calculated to form a force pair with the required force.
Required
Available
Ratio
Control
32,601 kN
56,549 kN
0.577
Bolt Bearing on Beam
20+2=22 mm
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Required
Available
Ratio
Control
64.748 kN
185,487 kN
0.349
Bolt Bearing on Plate
20+2=22 mm
ÇYTHYEDY 13.3.13
Required
Available
Ratio
Control
64.748 kN
284.75 kN
0.227
Plate Shear Yield
235.359 N/mm2
ÇYTHYEDY 13.17
Required
Available
Ratio
Control
64.748 kN
270 kN
0.240
Beam Shear Rupture
362.846 N/mm2
ÇYTHYEDY 13.18
Required
Available
Ratio
Control
64.748 kN
176.213 kN
0.367
Plate Shear Rupture
362.846 N/mm2
ÇYTHYEDY 13.18
Required
Available
Ratio
Control
64.748 kN
218.143 kN
0.297
Block Shear in Plate
235.359 N/mm2
362.846 N/mm2
one
ÇYTHYEDY 13.19
Required
Available
Ratio
Control
64.748 kN
229.569 kN
0.282
Plate Flexural Buckling
235.359 N/mm2
t
12 mm
a
60 mm
L
239 mm
λ
Required
Available
Control
≤0.70
0.17
Plate Flexural Yield
239 mm
235.359 N/mm2
12 mm
60 mm
Required
Available
Ratio
Control
64.748 kN
223.92 kN
0.289
Weld Strength at Support
in
12.73 mm
480 N/mm2
l
239 mm
is
60 mm
Required
Available
Ratio
Control
64.748 kN
421.131 kN
0.154
:check_mark: