End Plate Shear Connection Design per AISC 360-16
How does ideCAD design end plate shear connection according to AISC 360-16?
  • End plate shear connection limit states and geometry checks are done automatically according to AISC 360-16.
  • The block shear limit state is checked automatically according to AISC 360-16.
  • Limit state checks are made automatically according to AISC 360-16.
Ag: Gross area
An: Net cross-section area
Aw: Cross-section web area
Cv: Coefficient of reduction for shear buckling
d: Characteristic diameter of the stem of the bolt (the diameter of the non-threaded stem of the bolt)
dh: Bolt hole diameter
nsp: Number of slip planes
L: Connector distance
t: Plate thickness
Rn: Characteristic strength
Rnt: Characteristic tensile strength
Rnv: Characteristic shear strength
Ubs: A coefficient considering the spread of tensile stresses
Connection Geometry
Geometry Checks
Bolt Spacing
The distance between the centers of bolts is checked per AISC 360-16.
smin ≥ 3d
AISC 360-16 J3.3
s
60 mm
d
20 mm
s =60 mm > smin = 3*16=48 mm
Horizontal Edge Distance
Leh ≥ Le-min
AISC 360-16 J3.4
Leh
40 mm
Leh ≥ 2d = 2 * 16 = 32 mm conformity check for application
Le- min
22 mm
Vertical Edge Distance
Lev ≥ Le-min
AISC 360-16 J3.4
Lev
45 mm
Lev ≥ 2d = 2 * 16 = 32 mm conformity check for application
Le-min
22 mm
Welding Thickness
w ≥ wmin
w
7.072mm
wmin
5 mm
Table J2.4
Erection Stability
L ≥ hb /  2
L
150 mm
hb
190.4 mm
L=150 > 190.4/2=95.2 mm
Strength Checks
Bolt Shear at Support
The calculation is made using the Elastic method, one of the methods selected in the steel analysis settings tab. For the details of this check, AISC Manual 14th 7-8 is used as a reference.
In this check, the operation is performed on half of the symmetry axis and is calculated to form a force pair with the required force.
Ab
Fnv
Rn
AISC 360-16 J3-1
R n / Ω
Required
Available
Check
Result
31.564 kN
144.765 kN
0.218
Bolt Bearing on Support
Bearing strength limit states of the connection part that are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts are checked according to AISC 360-16.
dh
16+2=18 mm
Rn
AISC 360-16 J3-6a
Lc,spacing
Rn-spacing
Rn / Ω
Required
Available
Check
Result
31.564 kN
197,853 kN
0.160
Bolt Bearing on Plate
dh
16+2=18 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
Rn / Ω
Required
Available
Check
Result
31.564 kN
334,399 kN
0.094
Beam Shear Yield
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear yielding is checked according to AISC 360-16.
Ag
Fy
235.359 N/mm2
Rn
AISC 360-16 J4-3
Rn / Ω
Required
Available
Check
Result
31.564 kN
122.166 kN
0.258
Plate Shear Yield
Ag
Fy
235.359 N/mm2
Rn
AISC 360-16 J4-3
Rn / Ω
Required
Available
Check
Result
31.564 kN
338.77 kN
0.093
Plate Shear Rupture
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear rupture is checked according to AISC 360-16.
Anv
Fu
362.846 N/mm2
Rn
AISC 360-16 J4-4
Rn / Ω
Required
Available
Check
Result
31.564 kN
287,374 kN
0.110
Plate Block Shear Rupture
The block shear limit state is checked according to AISC 360-16. All block shear modes combined with tensile failure on one plane and shear failure on a perpendicular plane are checked according to AISC 360-16.
Ag
Anv
Ant
Fy
235.359 N/mm2
Fu
362.846 N/mm2
Ubs
1.0
Rn
AISC 360-16 J4-5
Rn / Ω
Required
Available
Check
Result
31.564 kN
308.556 kN
0.102
Welding Strength
Fe
480 N/mm2
w
7.07 mm
Fu
362.846  N/mm2
t
6.2 mm
l
135.856 mm
Rnw
RnBM
Rn
Rn / Ω
Required
Available
Check
Result
31.564 kN
91.688 kN
0.344