Splice Connection Design
A splice connection design is a moment-transmitting connection formed by bolted or welded connecting plates of beam caps and bodies. It can be used as a beam attachment or column attachment. Bolt control, welding control, and plate control are made automatically according to the placement of the connection elements.
The splice connection design in ideCAD Structural is automatically made according to the Design, Calculation, and Construction Principles of Steel Structures AISC 360-16 regulations and the connection report is created.
:check_mark:
Download ideCAD for Connection Design with AISC 360-16
Get Started FREE Software for Steel Connections
In the calculation of the splice connection, the distance between the header and the body bolts, the horizontal and vertical edge distance, and the welding control are made under the geometry control. In strength control, heading and body bolts slip, cap and body bolt hole crushing, beam cap and body bolt hole crushing, header plate tensile yield and tensile failure, head plate block slip, beam head block slip, head plate pressure leak, body plate block slip and weld control.
Connection Geometry
Geometry Checks
Bolt Spacing at Flange
ÇYTHYEDY 13.3.6
72 mm
24 mm
s =79.5 mm > smin = 3*24=72 mm
Horizontal Edge Distance at Flange
ÇYTHYEDY 13.3.7
75 mm
L eh ≥ 2d = 2 * 24 = 48 mm conformity check for application
32 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance at Flange
ÇYTHYEDY 13.3.7
35 mm
32 mm
Bolt Spacing at Web
ÇYTHYEDY 13.3.6
112.5 mm
32 mm
s =112.5 mm > smin = 3*24=72 mm
Horizontal Edge Distance at Web
ÇYTHYEDY 13.3.7
55 mm
32 mm
Vertical Edge Distance at Web
ÇYTHYEDY 13.3.7
50 mm
32 mm
Checks
Bolt Shear at Flange
Required
Available
Ratio
Control
315,683 kN
732.87 kN
0.431
Bolt Bearing on Flange Plate
24+2=26 mm
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Required
Available
Ratio
Control
315,683 kN
1371.558 kN
0.230
Bolt Bearing on Beam Flange
24+2=26 mm
ÇYTHYEDY 13.3.13
Required
Available
Ratio
Control
315,683 kN
1234,402 kN
0.256
Flange Plate Shear Yield
235.359 N/mm2
ÇYTHYEDY 13.15
Required
Available
Ratio
Control
281.974 kN
571.92 kN
0.493
Flange Plate Tensile Rupture
362.846 N/mm2
1.00
ÇYTHYEDY 13.16
Required
Available
Ratio
Control
281.974 kN
506.17 kN
0.557
FlangFlange Plate Block Shear
235.359 N/mm2
362.846 N/mm2
one
ÇYTHYEDY 13.19
Required
Available
Ratio
Control
281.974 kN
867,285 kN
0.325
235.359 N/mm2
362.846 N/mm2
one
ÇYTHYEDY 13.19
Required
Available
Ratio
Control
281.974 kN
780.55 kN
0.361
Beam Flange Block Shear
TO
0.65
L
150 mm
r
4.33 mm
22.52
235.359 N/mm2
ÇYTHYEDY 13.19
Required
Available
Ratio
Control
315,683 kN
571.92 kN
0.552
Bolt Shear at Web
Fn
Required
Available
Ratio
Control
0.458 kN
244.29 kN
0.002
Bolt Bearing on Web Plate
24+2=26 mm
ÇYTHYEDY 13.3.13
Required
Available
Ratio
Control
0.458 kN
241.656 kN
0.002
Bolt Bearing on Beam Web
24+2=26 mm
ÇYTHYEDY 13.3.13
Required
Available
Ratio
Control
0.458 kN
117.954 kN
0.004
Web Plate Shear Yield
A g
235.359 N/mm2
ÇYTHYEDY 13.17
Required
Available
Ratio
Control
1,108 kN
917.9 kN
0.001
Web Plate Shear Rupture
A nv
362.846 N/mm2
ÇYTHYEDY 13.17
Required
Available
Ratio
Control
1,108 kN
787,013 kN
0.001
Beam Shear Rupture
362.846 N/mm2
ÇYTHYEDY 13.17
Required
Available
Ratio
Control
1,108 kN
443,732 kN
0.002
Web Plate Block Shear
235.359 N/mm2
362.846 N/mm2
one
ÇYTHYEDY 13.19
Required
Available
Ratio
Control
1,108 kN
805,664 kN
0.001
:check_mark: