Double Angle Connection Design per AISC 360-16
How does ideCAD design single angle connection according to AISC 360-16?
  • Double angle connection limit states and geometry checks are done automatically according to AISC 360-16.
  • The block shear limit state is checked automatically according to AISC 360-16.
  • Limit state checks are made automatically according to AISC 360-16, depending on whether the connection type selected by the user is bolted or welded.
Ag: Gross area
An: Net cross-section area
Aw: Cross-section web area
Cv: Coefficient of reduction for shear buckling
d: Characteristic diameter of the stem of the bolt (the diameter of the non-threaded stem of the bolt)
dh: Bolt hole diameter
nsp: Number of slip planes
L: Connector distance
t: Plate thickness
Rn: Characteristic strength
Rnt: Characteristic tensile strength
Rnv: Characteristic shear strength
Ubs: A coefficient considering the spread of tensile stresses
Connection Geometry
Geometry Checks
Bolts Spacing
The distance between the centers of bolts is checked per AISC 360-16.
smin ≥ 3d
AISC 360-16 J3.3
s
79.5 mm
d
20 mm
s =79.5 mm > smin = 3*20=60 mm
Horizontal Edge Distance
Leh ≥ Le-min
AISC 360-16 J3.4
Leh
50.75 mm
L eh ≥ 2d = 2 * 20 = 40 mm conformity check for application
Le-min
26 mm
Vertical Edge Distance
Lev ≥ Le- min
AISC 360-16 J3.4
Lev
40 mm
Le- min
26 mm
Weld Size
a ≥ a min
a
7.072 mm
amin
5 mm
Table J2.4
Erection Stability
L ≥ hb /  2
L
239 mm
hb
248.6 mm
L=239 > 248.6/2=124.3 mm
Strength Checks
Angle Shear Yield
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear yielding is checked according to AISC 360-16.
Ag
Fy
235.359 N/mm2
Rn
AISC 360-16 J4-3
Rn / Ω
Required
Available
Check
Result
73.288 kN
540 kN
0.136
Beam Shear Rupture
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear rupture is checked according to AISC 360-16.
Anv
Fu
362.846 N/mm2
Rn
AISC 360-16 J4-4
Rn / Ω
Required
Available
Check
Result
73.288 kN
176.213 kN
0.416
Angle Shear Rupture at Beam
Anv
Fu
362.846 N/mm2
Rn
AISC 360-16 J4-4
Rn / Ω
Required
Available
Check
Result
73.288 kN
436,286 kN
0.168
Angle Block Shear at Beam
The block shear limit state is checked according to AISC 360-16. All block shear modes combined with tensile failure on one plane and shear failure on a perpendicular plane are checked according to AISC 360-16.
Ag
Anv
Ant
Fy
235.359 N/mm2
Fu
362.846 N/mm2
Ubs
1.0
Rn
AISC 360-16 J4-5
Rn / Ω
Required
Available
Check
Result
73.288 kN
505.94 kN
0.145
Bolt Bearing on Beam
Bearing strength limit states of the connection plate that are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts are checked according to AISC 360-16.
dh
20+2=22 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
Rn / Ω
Required
Available
Check
Result
73.288 kN
185,487 kN
0.395
Bolt Bearing on Angle at Beam
dh
20+2=22 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
Rn / Ω
Required
Available
Check
Result
73.288 kN
569.505 kN
0.129
Bolt Shear at Beam
The calculation is made using the Elastic method, one of the methods selected in the steel analysis settings tab. For the details of this check, AISC Manual 14th 7-8 is used as a reference.
In this check, the operation is performed on half of the symmetry axis and is calculated to form a force pair with the required force.
Ab
Fn
Rn
Rn / Ω
Required
Available
Check
Result
40.195
113.097 kN
0.355
Weld Strength at Support
Fe
480000 kN/m2
w
7.072
Fu
362.846  N/mm2
l
239 mm
Rn
Rn / Ω
Required
Ready
Rate
Control
73.288 kN
171.6 kN
0.427