Tipping Shear Force Range Control of Shearwalls per ASCE 7-16 with ideCAD
How does ideCAD control seismic force resisting ratio, according to ASCE 7-16, for two earthquake directions?
It’s automatically controlled and reported whether the moment frames resist at least 25% of the design seismic forces.
12.2.5.1 Dual System
Dual System is defined as A structural system with an essentially complete space frame providing support for vertical loads. Seismic force resistance is provided by moment-resisting frames and shear walls or braced frames.
For a dual system, the moment frames should be greater than or equal to 25% of the design seismic forces. It’s automatically controlled and reported whether the moment frames resist at least 25% of the design seismic forces.
12.2.5.4 Increased Structural Height Limit for Steel Eccentrically Braced Frames, Steel Special Concentrically Braced Frames, Steel Buckling-Restrained Braced Frames, Steel Special Plate Shear Walls, and Special Reinforced Concrete Shear Walls
In Table 12.2-1, it is permitted to increase the limits of structural height, hn from
  • 160 ft (50 m) to 240 ft (75 m) for structures assigned to Seismic Design Categories D or E
  • 100 ft (30 m) to 160 ft (50 m) for structures assigned to Seismic Design Category F,
Above conditions are controlled automatically to increase the limits.
12.2.5.8 Shear Wall–Frame Interactive Systems
The shear strength of the shear walls of the shear wall–frame interactive system should be greater than or equal to 75% of the design story shear at each story. The frames of the shear wall–frame interactive system should resist at least 25% of the design story shear in every story.
Structural System Type
Response Modification Coefficient, R
Overstrengh Factor, Ωo
Deflection Amplification Factor, Cd
Structural System Limitations Including Structural Height, hn (ft) Limits
B
C
D
E
F
A. Bearing Wall Systems
A1 - Special reinforced concrete shear walls
5
21/2
5
NL
NL
160
160
100
A2 - Ordinary reinforced concrete shear walls
4
21/2
4
NL
NL
NP
NP
NP
A3 - Detailed plain concrete shear walls
2
21/2
2
NL
NP
NP
NP
NP
A4 - Ordinary plain concrete shear walls
11/2
21/2
11/2
NL
NP
NP
NP
NP
B. Building Frame Systems
B1 - Steel eccentrically braced frames
8
2
4
NL
NL
160
160
100
B2 - Steel special concentrically braced frames
6
2
5
NL
NL
160
160
100
B3 - Steel ordinary concentrically braced frames
31/4
2
31/4
NL
NL
35
35
NP
B4 - Special reinforced concrete shear walls
6
21/2
5
NL
NL
160
160
100
B5 - Ordinary reinforced concrete shear walls
5
21/2
41/2
NL
NL
NP
NP
NP
B6 - Detailed plain concrete shear walls
2
21/2
2
NL
NP
NP
NP
NP
B7 - Ordinary plain concrete shear walls
11/2
21/2
11/2
NL
NP
NP
NP
NP
C. Moment-Resisting Frame Systems
C1 - Steel special moment frames
8
3
51/2
NL
NL
NL
NL
NL
C2 - Steel special truss moment frames
7
3
51/2
NL
NL
160
100
NP
C3 - Steel intermediate moment frames
41/2
3
4
NL
NL
35
NP
NP
C4 - Steel ordinary moment frames
31/2
3
3
NL
NL
NP
NP
NP
C5 - Special reinforced concrete moment frames
8
3
51/2
NL
NL
NL
NL
NL
C6 - Intermediate reinforced concrete moment frames
5
3
41/2
NL
NL
NP
NP
NP
C7 - Ordinary reinforced concrete moment frames
3
3
21/2
NL
NP
NP
NP
NP
D. Dual Systems with Special Moment Frames Capable of Resisting at Least 25% of Prescribed Seismic Foces
D1 - Steel eccentrically braced frames
8
21/2
4
NL
NL
NL
NL
NL
D2 - Steel special concentrically braced frames
7
21/2
51/2
NL
NL
NL
NL
NL
D3 - Special reinforced concrete shear walls
7
21/2
51/2
NL
NL
NL
NL
NL
D4 - Ordinary reinforced concrete shear walls
6
21/2
5
NL
NL
NP
NP
NP
E. Dual Systems with Intermediate Moment Frames Capable of Resisting at Least 25% of Prescribed Seismic Foces
E1 - Steel special concentrically braced frames
6
21/2
5
NL
NL
35
NP
NP
E2 - Special reinforced concrete shear walls
61/2
21/2
5
NL
NL
160
100
100
E8 - Ordinary reinforced concrete shear walls
51/2
21/2
41/2
NL
NL
NP
NP
NP
F. Shear Wall-Frame Interactive System with Ordinary Reinforced Concrete Moment Frames And Ordinary Reinforced Concrete Shear Walls
F1 - Shear wall-frame interactive system
41/2
21/2
4
NL
NP
NP
NP
NP
G. Cantilevered Column Systems Detailed to Conform to the Requirement for
G1 - Steel special cantilever column systems
21/2
11/4
21/2
35
35
35
35
35
G2 - Steel ordinary cantilever column systems
11/4
11/4
11/4
35
35
NP
NP
NP
G3 - Special reinforced concrete moment frames
21/2
11/4
21/2
35
35
35
35
35
G4 - Intermediate reinforced concrete moment frames
11/2
11/4
11/2
35
35
NP
NP
NP
G5 - Ordinary reinforced concrete moment frames
1
11/4
1
35
NP
NP
NP
NP
H. Steel Systems not Specifically Detailed for Seismic Resistance, Excluding Cantilever Column Systems
H - Steel Systems not Specifically Detailed for Seismic Resistance
3
3
3
NL
NL
NP
NP
NP