Bolted Flange Plate Connection Design per AISC 358-16 & AISC 360-16
How does ideCAD design Bolted Flange Plate Connections according to AISC 358-16 & AISC 360-16?
  • Design limit states of bolted flange plate connections are calculated automatically according to AISC 358-16 and AISC 360-16.
Ag: Gross area
An: Net cross-section area
Aw: Cross-section web area
bp = width of end-plate, in. (mm)
g = horizontal distance between bolts, in. (mm)
dh: Bolt hole diameter
nsp: Number of slip planes
L: Connector distance
pb = vertical distance between the inner and outer row of bolts in an eight-bolt stiffened connection, in. (mm)
pfi = vertical distance from the inside of a beam tension flange to the nearest inside bolt row, in. (mm)
pfo = vertical distance from the outside of a beam tension flange to the nearest outside bolt row, in. (mm)
tbf = thickness of beam flange, in. (mm)
Rn: Characteristic strength
Connection Geometry
GEOMETRY CHECKS
Bolt Spacing at Flange
The distance between the centers of bolts is checked per AISC 360-16.
smin ≥ 3d
AISC 360-16 J3.3
s
84 mm
d
27 mm
s =84 mm > smin = 3*27=81 mm
Horizontal Edge Distance at Flange
The distance from the center of the bolt hole to the edge of the connected part in the horizontal direction is checked per AISC 360-16.
Le ≥ Le-min
AISC 360-16 J3.4
Le
60 mm
Le ≥ 2d = 2 * 27 = 54 mm conformity check for application
Le-min
34 mm
Vertical Edge Distance at Flange
The distance from the center of the bolt hole to the edge of the connected part in the vertical direction is checked per AISC 360-16.
L e ≥ Le-min
AISC 360-16 J3.4
Le
50 mm
Check suitability for L e ≥ 2d = 2 * 27 = mm application
Le- min
34 mm
Bolt Spacing at web
smin ≥ 3d
AISC 360-16 J3.3
s
72 mm
d
24 mm
s =7 mm > smin = 3*24=72 mm
Horizontal Edge Distance at web
Le ≥ Le-min
AISC 360-16 J3.4
Le
90 mm
Conformity check for Le ≥ 2d = 2 * 24 = 48 mm application
Le-min
30 mm
Vertical Edge Distance at web
Le ≥ Le-min
AISC 360-16 J3.4
Le
60 mm
L eh ≥ 2d = 2 * 24 = 48 mm conformity check for application
Le-min
30 mm
Shear Plate to Column Flange Weld Size
w ≥ wmin
w
11.315 mm
wmin
5 mm
Table J2.4
w ≥ wmin
w
11.315 mm
wmin
6 mm
Table J2.4
w ≥ wmin
w
11.315 mm
wmin
6 mm
Table J2.4
PREQUALIFICATION LIMITS
Beam span / Beam cross-section height
9144 mm /550 mm=16.63
≥9.0
Beam cross-section height, db
550 mm
≤ 920
Beam head thickness, tbf
17.2 mm
≤25
Column cross-section height
650 mm
≤ 920 mm
Bolt class
8.8
8.8 - 10.9
Bolt size
M27
≤ M27
Min yield stress of flange plate material
275 MPa
235 /275 / 355 MPa
Flange plate weld
CJP
CJP
STRENGTH CHECKS
Bolt diameter
The required bolt diameter, db, for bolted flange plate connection is checked according to AISC 358-16 §7.6
bf
210 mm
AISC 358-16 7.6-2
Ry
1.40
Fy
235 N/mm2
Rt
1.10
Fu
360 N/mm2
db
db
Required
Available
Ratio
Control
14.765 mm
27 mm
1.829
Bolt Shear at Flange
The shear limit state of plate bolts is checked according to AISC 360-16.
Ab
AISC 360-16 J3-1
Fn
Rn
ΦRn
Required
Available
Ratio
Control
2097.19 kN
1855.079 kN
1.131
Bolt Bearing on Flange Plate
Bearing strength limit states of the connection plate that are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts are checked according to AISC 360-16.
dh
27+3=30 mm
Lc,edge
Rn
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
2097.19 kN
5866.214 kN
0.358
Bolt Bearing on Beam Flange
dh
27+3=30 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
2097.19 kN
2768.57 kN
0.758
Flange Plate Tension Yield
The yield limit state of the connection plate is checked according to AISC 360-16.
Ag
Fy
275 N/mm2
Rn
AISC 360-16 J4-1
ΦRn
Required
Available
Ratio
Control
2097.19 kN
1848 kN
1.135
Flange Plate Tension Rupture
The limit state of the flange plate tension rupture is checked according to AISC 360-16.
An
Ae
Fu
410 N/mm2
U
1.00
Rn
AISC 360-16 J4-2
ΦRn
Required
Available
Ratio
Control
2097.19 kN
1723.968 kN
1.216
Flange Plate Block Shear
The block shear limit state is checked according to AISC 360-16. All block shear modes combined with tensile failure on one plane and shear failure on a perpendicular plane are checked according to AISC 360-16.
Ag
Anv
Ant
Fy
275 N/mm2
Fu
410 N/mm2
Ubs
1.0
Rn
AISC 360-16 J4-5
ΦRn
Required
Available
Ratio
Control
2097.19 kN
3636.864 kN
0.577
Beam Flange Block Shear
Ag
Anv
Ant
Fy
235 N/mm2
Fu
360 N/mm2
Ubs
1.0
Rn
AISC 360-16 J4-5
ΦRn
Required
Available
Ratio
Control
2097.19 kN
1716.42 kN
1.222
Bolt Shear Rupture at Web
The shear limit state of end plate bolts is checked according to AISC 360-16.
Ab
AISC Manual 14th 7-8
Fn
Rn
ΦRn
Required
Available
Ratio
Control
132.193 kN
183.218 kN
0.722
Bolt Bearing on Beam Web
dh
24+3=27 mm
Rn
AISC 360-16 J3-6a
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
361.984 kN
971.028 kN
0.373
Bolt Bearing on Web Plate
dh
24+2=26 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
361.984 kN
1206.187 kN
0.300
Web Plate Shear Yield
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear yielding is checked according to AISC 360-16.
Ag
Fy
275 N/mm2
Rn
AISC 360-16 J4-3
ΦRn
Required
Available
Ratio
Control
361.984 kN
807.84 kN
0.448
Web Plate Shear Rupture
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear rupture is checked according to AISC 360-16.
Anv
Fu
410 N/mm2
Rn
AISC 360-16 J4-4
ΦRn
Required
Available
Ratio
Control
361.984 kN
698.738 kN
0.518
Beam Shear Rupture
Anv
Fu
360 N/mm2
Rn
AISC 360-16 J4-4
ΦRn
Required
Available
Ratio
Control
361.984 kN
873.925 kN
0.414
Web Plate Block Shear
Ag
Anv
Ant
Fy
275 N/mm2
Fu
410 N/mm2
Ubs
1.0
Rn
AISC 360-16 J4-5
ΦRn
Required
Available
Ratio
Control
361.984 kN
912.168 kN
0.397
dp
408 mm
F y
275 N/mm2
t p
12 mm
a
110 mm
Rn
AISC 360-16 J4-5
ΦRn
Required
Available
Ratio
Control
361.984 kN
728.794 kN
0.338
Shear Plate to Column Flange Weld Strength
w
11.315 mm
FE
490 N/mm2
l
408 mm
e
110 mm
Rn
ΦRn
Required
Available
Ratio
Control
361.984 kN
1152.2 kN
0.314
Column Panel Zone Shear
The panel zone shear limit state for the bolted flange plate connection is checked according to AISC 358-16 §7.6.
Pr
429.124 kN
AISC 360-16 J10-9
Py
Fy
275000 kN/m2
Ag
28634.759 mm2
dc
650 mm
tw
16 mm
Rn
ΦRn
Required
Available
Ratio
Control
1776.832 kN
1716 kN
1.035
Panel Zone Thickness
The required panel zone thickness for bolted flange plate connection is checked according to AISC 358-16 §7.6
tmin ≥u / 180
tmin = tw
16 mm
tw
16 mm
u
2207.2 mm
Required
Available
Ratio
Control
12.262 mm
16 mm
0.766