4 Bolts Unstiffened End Plate Connection Design per AISC 358-16 & AISC 360-16
How does ideCAD design Four Bolts Unstiffened End Plate Connection according to AISC 358-16 & AISC 360-16?
  • Four bolts unstiffened end plate connection is designed automatically according to the AISC 358-16 and AISC 360-16 by the ideCAD Structural.
Ag: Gross area
An: Net cross-section area
Aw: Cross-section web area
bp = width of end-plate, in. (mm)
g = horizontal distance between bolts, in. (mm)
dh: Bolt hole diameter
nsp: Number of slip planes
L: Connector distance
pb = vertical distance between the inner and outer row of bolts in an eight-bolt stiffened connection, in. (mm)
pfi = vertical distance from the inside of a beam tension flange to the nearest inside bolt row, in. (mm)
pfo = vertical distance from the outside of a beam tension flange to the nearest outside bolt row, in. (mm)
tbf = thickness of beam flange, in. (mm)
Rn: Characteristic strength
Rnt: Characteristic tensile strength
Rnv: Characteristic shear strength
Connection Geometry
GEOMETRY CHECKS
Horizontal Edge Distance
Leh ≥ Le-min
AISC 360-16 J3.4
Leh
70 mm
Leh ≥ 2d = 2 * 30 = 60 mm conformity check for application
Le-min
38 mm
Vertical Edge Distance
Lev ≥ Le-min
AISC 360-16 J3.4
Lev
85 mm
L eh ≥ 2d = 2*30 = 60 mm conformity check for application
Le-min
38 mm
Beam web to End Plate Weld Size
w ≥ wmin
w
8.487 mm
wmin
5 mm
w ≥ wmin
w
11.315 mm
wmin
6 mm
w ≥ wmin
w
11.315 mm
wmin
6 mm
Prequalification Limits (AISC 358 -16 Table 6.1)
All end-plate moment connection configurations should satisfy these beam and column limitations. Beam and column limitations are given in AISC 358-16 Table 6.1.
Beam span / Beam cross-section height
9144 mm /450 mm = 20.32
≥7.0
End plate thickness, tp
32 mm
13≤tp ≤57
End plate width, bp
290 mm
178≤ bp ≤ 273
Horizontal distance between bolts, g
150 mm
102≤g≤152
pfi
60 mm
38≤pfi ≤114
pfo
60 mm
38≤pfo ≤114
Beam depth, db
450 mm
349≤ db ≤ 1400
Beam flange thickness, tbf
15 mm
10≤tbf ≤19
Beam flange width, bbf
190
152≤bbf ≤235
Column depth
650
≤ 920 mm
Bolt grade
10.9
8.8 - 10.9
Min yield stress of the end plate material
275 MPa
235 /275 / 355 MPa
Flange plate weld
CJP
CJP
Strength Checks
Bolt diameter
The required bolt diameter, db, for four bolts unstiffened end plate connection is checked according to AISC 358-16 §6.8
Muc
796.489 kNm
AISC 358-16 (6.8-3)
Ft
750 N/mm2
ho
h1
db
Required
Available
Ratio
Control
29.385 mm
30 mm
0.979
End Plate Thickness
The required end plate thickness, tb, for four bolts unstiffened end plate connection is checked according to AISC 358-16 §6.8
Muc
796.489 kNm
AISC 358-16 (6.8-5)
Fyp
275 N/mm2
s
Yp
Yp
tp
Required
Available
Ratio
Control
30.997 mm
32 mm
0.969
End Plate Shear Yield
The shear yielding of the end plate is checked according to AISC 358-16 §6.8.
Muc
796.489 kNm
AISC 358-16 (6.8-7)
Ff
Rreq = Ff / 2
Fyp
275 N/mm2
bp
290 mm
tp
32 mm
d
450 mm
tbf
15 mm
Rn
Required
Available
Ratio
Control
915.504 kN
1531.2 kN
0.598
End Plate Shear Rupture
The shear rupture of the end plate is checked according to AISC 358-16 §6.8.
Muc
796.489 kNm
AISC 358-16 (6.8-7)
Ff
R req = Ff / 2
Fup
410 N/mm2
An
d
450 mm
tbf
15 mm
Rn
ΦRn
Required
Available
Ratio
Control
915.504 kN
1027.3 kN
0.891
Bolt Shear Check
The shear limit state of end plate bolts is checked according to AISC 360-16.
Ab
Fn
Rn
ΦRn
Required
Available
Ratio
Control
270.986 kN
1145.11 kN
0.237
Bolt Bearing on End Plate
Bearing strength limit states of the connection plate that are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts are checked according to AISC 360-16.
dh
30+3=33 mm
Lc,edge
Rn
AISC 358-16 6.8-12
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
270.986 kN
3400.704 kN
0.08
Bolt Bearing on Column Flange
dh
30+3=33 mm
Rn
AISC 358-16 6.8-12
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
270.986 kN
3294.432 kN
0.082
Beam Web to End Plate Weld Size
The required end weld size for four bolts unstiffened end plate connection is checked according to AISC 358-16 §6.7
Fyp
275000 kN/m2
AISC 358-16
6.7.6 (3)
tbw
9 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
4.763 mm
8.487 mm
0.561
Column Flange Thickness
The required column flange thickness, tcf, for four bolts unstiffened end plate connection is checked according to AISC 358-16 §6.8
Muc
796.489 kNm
AISC 358-16 (6.8-13)
Fyp
275 N/mm2
s
c
Yc
Yc
tcf
Required
Available
Ratio
Control
24.527 mm
31 mm
0.791
Column Panel Zone Shear
Yielding of the column panel zone for four bolts unstiffened end plate connection is checked according to AISC 360-16 §J.10
Pr
366.473 kN
AISC 360-16 J10-9
Py
Fy
275 N/mm2
A g
28634.759 mm2
d c
650 mm
tw
16 mm
Rn
ΦRn
Required
Available
Ratio
Control
1621.957 kN
1716 kN
0.945
Panel Zone Thickness
The required panel zone thickness for four bolts unstiffened end plate connection is checked according to AISC 358-16.
tmin ≥u/180
tmin = t w
16 mm
tw
16 mm
u
2016 mm
Required
Available
Ratio
Control
11.2 mm
16 mm
0.700