Splice Connection Design per AISC 360-16
How does ideCAD design Column/Beam splice connection according to AISC 360-16?
  • Column/Beam splice connection design limit states and geometry checks are done automatically according to AISC 360-16.
  • The block shear limit state is checked automatically according to AISC 360-16.
:check_mark:
Download ideCAD for Connection Design with AISC 360-16
Get Started FREE Software for Steel Connections
Ag: Gross area
An: Net cross-section area
d: Characteristic diameter of the stem of the bolt (the diameter of the non-threaded stem of the bolt)
dh: Bolt hole diameter
t: Plate thickness
Rn: Characteristic strength
Ubs: A coefficient considering the spread of tensile stresses
Connection Geometry
GEOMETRY CHECKS
Bolt Spacing at Flange
The distance between the centers of bolts is checked per AISC 360-16.
smin ≥ 3d
AISC 360-16 J3.3
s
72 mm
d
24 mm
s =72 mm > smin = 3*24=72 mm
Horizontal Edge Distance at Flange
Leh ≥ Le-min
AISC 360-16 J3.4
Leh
75 mm
Leh ≥ 2d = 2 * 24 = 48 mm conformity check for application
Le-min
30 mm
Vertical Edge Distance at Flange
Lev ≥ Le-min
AISC 360-16 J3.4
Lev
35 mm
Le- min
30 mm
Minimum distance check according to AISC 360-16 Table J3.4
Bolt Spacing at Web
smin ≥ 3d
AISC 360-16 J3.3
s
113 mm
d
24 mm
s =113 mm > smin = 3*24=72 mm
Horizontal Edge Distance at Web
Leh ≥ L e-min
AISC 360-16 J3.4
Leh
55 mm
Le-min
30 mm
Vertical Edge Distance at Web
Lev ≥ Le-min
AISC 360-16 J3.3
Lev
49.5 mm
L eh ≥ 2d = 2 * 24 = 48 mm conformity check for application
Le-min
30 mm
STRENGTH CHECKS
Bolt Shear at Flange
The calculation is made using the Elastic method, one of the methods selected in the steel analysis settings tab. In this check, the operation is performed on half of the symmetry axis and is calculated to form a force pair with the required force.
Ab
AISC 360-16 J3-1
Fn
Rn
ΦRn
Required
Ready
Rate
Control
425.018 kN
732.87 kN
0.580
Bolt Bearing on Flange Plate
The bearing strength limit states of the connection plate, which are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts, are checked according to AISC 360-16.
dh
24+3=27 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
425.018 kN
1341.36 kN
0.317
Bolt Bearing on Beam Flange
dh
24+3=27 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
418.114 kN
1305.591 kN
0.320
Flange Plate Tension Yield
The yield limit state of the connection plate subjected to tension is checked according to AISC 360-16.
Ag
Fy
235 N/mm2
Rn
AISC 360-16 J4-1
ΦRn
Required
Available
Ratio
Control
301.881 kN
571.92 kN
0.529
Flange Plate Tension Rupture
The limit state of the flange plate tension rupture is checked according to AISC 360-16.
An
Ae
Fu
360 N/mm2
U
1.00
Rn
AISC 360-16 J4-2
ΦRn
Required
Available
Ratio
Control
301.881 kN
494.1 kN
0.611
Flange Plate Block Shear
The block shear limit state is checked according to AISC 360-16. All block shear modes combined with tensile failure on one plane and shear failure on a perpendicular plane are checked according to AISC 360-16.
Ag
Anv
Ant
Fy
235 N/mm2
Fu
360 N/mm2
Ubs
1.0
Rn
AISC 360-16 J4-5
ΦRn
Required
Available
Ratio
Control
301.881 kN
860.828 kN
0.351
Beam Flange Block Shear
Ag
Anv
Ant
Fy
235 N/mm2
Fu
360 N/mm2
Ubs
1.0
Rn
AISC 360-16 J4-5
ΦRn
Required
Available
Ratio
Control
301.881 kN
837.867 kN
0.360
Flange Plate Compression Yield
The yield limit state of the connection plate subjected to compression is checked according to AISC 360-16.
K
0.65
L
150 mm
r
4.33 mm
KL / r
22.52
Fy
235 N/mm2
Ag
Rn
AISC 360-16 J4-6
ΦRn
Required
Available
Ratio
Control
418.114 kN
571.05 kN
0.732
Bolt Shear at Web
The shear limit state of end plate bolts is checked according to AISC 360-16.
Ab
Fn
Rn
AISC 360-16 J3-1
ΦRn
Required
Available
Ratio
Control
0.031 kN
244.29 kN
0.00013
Bolt Bearing on Web Plate
Bearing strength limit states of the connection plate that are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts are checked according to AISC 360-16.
dh
24+3=27 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Rn
ΦRn
Required
Available
Ratio
Control
0.031 kN
233.28 kN
0.0001
Bolt Bearing on Beam Web
dh
24+3=27 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Rn
ΦRn
Required
Available
Ratio
Control
0.031 kN
126.392 kN
0.00024
Web Plate Shear Yield
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear yielding is checked according to AISC 360-16.
Ag
Fy
235 N/mm2
Rn
AISC 360-16 J4-3
ΦRn
Required
Available
Ratio
Control
0.075 kN
916.5 kN
0.0001
Web Plate Shear Rupture
The shear strength of connecting elements in shear is the minimum value obtained according to the limit states of shear yielding and shear rupture. Shear rupture is checked according to AISC 360-16.
Anv
Ae
Fu
360 N/mm2
Rn
AISC 360-16 J4-4
ΦRn
Required
Available
Ratio
Control
0.075 kN
771.12 kN
0.0001
Beam Shear Rupture
Anv
Ae
Fu
360 N/mm2
Rn
AISC 360-16 J4-4
ΦRn
Required
Available
Ratio
Control
0.075 kN
552.76 kN
0.0001
Web Plate Block Shear
Ag
Anv
Ant
Fy
235 N/mm2
Fu
360 N/mm2
Ubs
1.0
Rn
AISC 360-16 J4-5
ΦRn
Required
Available
Ratio
Control
0.075 kN
801.38 kN
0.0001
:check_mark: