Brace Corner Connection Design
The brace corner connection is formed by bolting and welding the steel brace member to the column, beam or column-to-beam connection. Bolt control, weld control, plate control and connection application limits control are performed automatically according to the placement of the elements of the connection. Brace corner connection design is made automatically according to the Design, Calculation and Construction Principles of Steel Structures (ÇYTHYEDY) or AISC 360-16 regulations and a connection report is created.
In the brace corner connection calculation, horizontal and vertical bolt distances, end plate weld thickness, continuity plate weld thickness and application limits are checked under geometry control. In strength control, cross bolt slip, plate bolt hole crushing, ski control, Whitmore section buckling, plate pressure leakage are checked.
Connection Geometry
Brace - Gusset Plate Connection
Geometry Checks
Bolt Spacing
s min ≥ 3d
ÇYTHYEDY 13.3.6
s
60 mm
d
20 mm
s =60 mm > smin = 3*20=60 mm
Horizontal Edge Distance
L eh ≥ L e- min
ÇYTHYEDY 13.3.7
L eh
33.5 mm
L e- min
26 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance
L ev ≥ L e- min
ÇYTHYEDY 13.3.7
L ev
40 mm
Conformity check for L eh ≥ 2d = 2 * 20 = 40 mm application
L e- min
26 mm
Weld Size
a ≥ a min
ÇYTHYEDY 13.3.7
a
4 mm
a min
3.5 mm
Table 13.4
Strength Checks
Bolt Shear at Brace
A b
Fn
Rn
ΦRn
Required
Available
Ratio
Control
367,989 kN
424.115 kN
0.868
Bolt Bearing on Plate
d h
20+2=22 mm
Lc,edge
Rn
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
367,989 kN
906.912 kN
0.406
Bolt Bearing on Gusset
d h
20+2=22 mm
Lc,edge
Rn
ÇYTHYEDY 13.3.13
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
367,989 kN
566.82 kN
0.649
Weld Strength
Fe
490000 kN/m2
w
The weld thickness taken from the combination menu is 0.707 * w value. 4 / 0.707 = 5.658 mm
F u-plate
469.999  N/mm2
F u-brace
410 N/mm2
tplate
16 mm
t brace
10 mm
R nw
Rn-plate
Rn-brace
RnBM
Rn
ΦRn
Required
Available
Ratio
Control
367,989 kN
493.92 kN
0.745
Whitmore Section Buckling
K
0.65
L
153.5 mm
r
2.887 mm
KL / r
34.56
Fy
355 N/mm2
Ag
1881.409 mm2
Fe
Fcr
Rn
ΦRn
Required
Available
Ratio
Control
367,989 kN
549.42 kN
0.670
Gusset Axial Yield
K
0.65
L
60 mm
r
4.619 mm
KL / r
8.44
Fy
355 N/mm2
Ag
2991.995 mm2
Rn
ÇYTHYEDY 13.20
ΦRn
Required
Available
Ratio
Control
367,989 kN
955,942 kN
0.385
Gusset to Beam Connection
Geometry Checks
Weld Size
a ≥ a min
ÇYTHYEDY 13.3.7
a
4 mm
a min
3.5 mm
Table 13.4
Strength Checks
Gusset Axial Yield
F y
355 N/mm2
Z
F a
N
260,207 kN
M
10.775 kNm
tg
10 mm
l g
347.279 mm
F b
Fn
Rn
ΦRn
Required
Available
Ratio
Control
110666.08 kN/m2
319500 kN/m2
0.346
Gusset Shear Yield
F y
355 N/mm2
V
260,207 kN
tg
10 mm
l g
347.279 mm
Fv
Rn
ΦRn
Required
Available
Ratio
Control
74927.3 kN/m2
213000 kN/m2
0.352
Weld Strength
Fpeak
Favg
R req
ÇYTHYEDY 13.3
tg
10 mm
in
5.658 mm
F e
480000 kN/m2
θ
55.9 °
Rn
ΦRn
Required
Available
Ratio
Control
1363.764 kN/m
2428.6 kN/m
0.562