Welded Web Moment (WUF-W) Connection Design per AISC 358-16 & AISC 360-16
How does ideCAD design Welded Web (WUF-W) Moment Connections according to AISC 358-16 & AISC 360-16?
Design limit states of welded web connections are calculated automatically according to AISC 358-16 and AISC 360-16.
Ag: Gross area
An: Net cross-section area
Aw: Cross-section web area
bp = width of end-plate, in. (mm)
g = horizontal distance between bolts, in. (mm)
dh: Bolt hole diameter
nsp: Number of slip planes
K: Effective length factor
L: Connector distance
tbf = thickness of beam flange, in. (mm)
w = Size of weld leg, in. (mm)
Rn: Characteristic strength
Rnwl: Total nominal strength of longitudinally loaded fillet welds
Rnwt: Total nominal strength of transversely loaded fillet welds,
Connection Geometry
GEOMETRY CHECKS
Weld Access Hole Length
The maximum weld access hole length is checked per AISC 360-16.
L ≥ max( 1.5tw, 38 mm )
AISC 360-16 J1.7
L
50 mm
tw
9 mm
Weld Access Hole Height
The maximum weld access hole height is checked per AISC 360-16.
H ≥ max( tw, 19 mm ) , H≤50mm
AISC 360-16 J1.6
H
30 mm
tw
9 mm
Shear Plate to Column Flange Weld Size
w≥ wmin
w
12.73 mm
wmin
5 mm
Shear Plate to Beam Web Weld Size
w≥ wmin
w
8.487 mm
wmin
5 mm
w≥ wmin
w
11.315 mm
wmin
6 mm
Continuity Plate - Column Body Welding Thickness
w≥ wmin
w
11.315 mm
wmin
6 mm
PREQUALIFICATION LIMITS
Beam span / Beam cross-section height
9144 mm /450 mm=20.32
≥9.0
Beam cross-section
450 mm
≤ 920
Beam head thickness, tbf
15 mm
≤25
Column cross-section height
650 mm
≤ 920 mm
Flange plate weld
CJP
CJP
tp
10 mm
≥9 mm
a
10 mm
6≤a≤12
d
50 mm
≥50 mm
Shear plate beam web weld size
6 mm
=6 mm
Flange plate weld
CJP
CJP
STRENGTH CHECKS
Beam Shear Yield
The nominal and design yield strength of the web plate is checked according to AISC 360-16
Ag
Fy
275 N/mm2
Rn
AISC 360-16 J4-3
ΦRn
Required
Available
Ratio
Control
265.569 kN
534.6 kN
0.497
Shear Plate to Column Flange Weld Strength
The nominal and design weld strength for the shear plate to column weld is checked according to AISC 360-16
Fe
490000 kN/m2
AISC 360-16 J2-3
w
12.73 mm
l
380 mm
Rreq
hp
380 mm
tp
10 mm
Ry
1.30
Fyp
275 N/mm2
Rn
ΦRn
Required
Available
Ratio
Control
815.1 kN
904.94 kN
0.901
Column Panel Zone Shear
The welded web connection's panel zone shear limit state is checked according to AISC 360-16.
Pr
429.124 kN
AISC 360-16 J10-9
Py
F y
275000 kN/m2
A g
28634.759 mm2
dc
650 mm
tw
16 mm
Rn
ΦRn
Required
Available
Ratio
Control
1497.795 kN
1716 kN
0.873
Panel Zone Thickness
The required panel zone thickness for welded web connection is checked according to AISC 358-16.
tmin ≥u / 180
tmin = tw
16 mm
tw
16 mm
u
2016 mm
Required
Available
Ratio
Control
11.2 mm
16 mm
0.700