Architecture & Structural Engineering

Shearwall Reinforcements

Shearwall reinforcement design results and inadequacy of shears are displayed in the Shearwall Reinforcement dialog. In the shearwall reinforcement dialog, shearwall transverse and longitudinal reinforcements, head zone reinforcements, internal forces calculated as a result of the analysis, increased internal forces related to TBDY, and capacity ratio results are given. The body and head area reinforcements of the shearwalls can be changed and fixed in the Shearwall Reinforcement dialog.

Location of Shearwall Reinforcements Dialog

After analysis, you can access it by clicking on the Shearwall Reinforcements command under the Concrete Design title of the ribbon menu Analysis and Design tab .

image-20210127-062318.png

General Specifications of Shearwall Reinforcements Dialogue

Summary Information

The summary information about the line where the cursor is located is given in the form of story name, in the name section of the dialog.

image-20210127-062554.png

For example Base Story, P1

Using the Shift key

In this tab, you can select more than one row with the Shift key, enter a value by double-clicking any cell whose value is open to change, and you can make that value apply to all selected rows.

Using the Ctrl key

Ctrl key, on the other hand, selects the lines in between one by one.

Reinforcement calculator

image-20210126-101223.png

Calculates the amount of rebar, in area, for the selected diameter and span.

Show only reinforcement shearwalls

image-20210127-062715.png

It only lists the rebar shearwalls.

All Stories

image-20210126-073405.png

It lists the slabs on the screen throughout the entire story.

Select

image-20210126-074842.png

Selects the object on the line with the cursor. When the concrete dialog is closed, you can take action for the selected element.

Previous

image-20201127-071208.png

The cursor moves to the previous line.

Next

image-20201127-071333.png

The cursor goes to the next line.

Filter

image-20210126-074904.png

It is used to define certain conditions and filter only the elements that satisfy that condition.

Recalculate

image-20210126-101356.png

The element rebuilds its concrete. The regulation calculations related to concrete and rebars are also made again. It may be more appropriate to repeat the structure analysis instead of concrete in important changes.

Ok

image-20240314-081618.png

It saves the changes made and closes the dialog.

Cancel

image-20240314-081627.png

Closes the dialog without saving the changes made.

Insufficiency Code

Description

K

Shear safety is not satisfied.
The wall fails to meet the required shear capacity. Solutions: Increase wall thickness; enhance shear reinforcement by increasing stirrup diameter or reducing spacing.

F

Friction-based shear capacity is not satisfied.
Solutions: Increase longitudinal reinforcement; enlarge wall cross-sectional dimensions; improve confinement detailing.

E

The maximum axial load capacity is exceeded.
Solutions: Increase wall dimensions; use higher-strength concrete; reduce applied axial loads through structural redesign.

M

The maximum reinforcement ratio is exceeded.
The reinforcement ratio surpasses code limits. Solutions: Reduce the amount of reinforcement; adjust wall dimensions to comply with code limits.

ab

The hook development length is not satisfied as per the Seismic Design Code.
Solutions: Increase the smaller dimension of the wall; improve rebar anchorage detailing; consider increasing wall width or height; use smaller diameter longitudinal reinforcement; use higher-strength concrete.

As(-)

The provided longitudinal reinforcement is insufficient.
Solutions: Choose larger diameter bars and increase the number of bars to meet the required area.

As(-)B

Transverse reinforcement in the wall boundary region is insufficient.
Solutions: Reduce stirrup spacing; increase stirrup diameter; ensure compliance with code requirements for transverse reinforcement.

Z

Punching shear capacity is exceeded (typically in slab-wall connections).
Solutions: Increase slab thickness; provide drop panels or shear capitals; add punching shear reinforcement.

T

The transfer of seismic forces from the slab to the wall is not satisfied according to the Seismic Design Code.
Solutions: Improve connection detailing between slab and wall; ensure adequate reinforcement to transfer seismic forces.

W

Strong wall condition is not satisfied according to the Seismic Design Code.
Solutions: Adjust wall dimensions to satisfy hw/lw > 2 condition; ensure compliance with code requirements for strong walls.

R

The capacity ratio under axial load and biaxial bending exceeds 1.0.
Solutions: Redesign the wall to reduce demand, increase capacity through reinforcement or section modification, or consider using higher-strength materials.

Shearwalls Tab

image-20240314-061737.png

Specifications

DS

image-20201229-144432.png

If marked, the rebar is fixed. When the shearwall is changed, DS is automatically marked and when concrete is made, the shearwall also remains constant. If DS is not marked, when concrete is made, shearwall rebar is determined again according to rebar selection conditions. .

ID

image-20240314-061936.png

It is the name of the shearwall in the plan. (P1, P101, P10 etc.) In case of negativity, a term related to negativity is added next to the name. Like P101 (E) ..

Story

image-20240314-061951.png

Indicates the story where the shearwall is located.

B

image-20240314-062007.png

It is the width of the shearwall.

lw

image-20240314-062022.png

It is the length of the shearwall.

HeadL

image-20240314-062039.png

It is the value of the rebar in the left region in terms of quantity and diameter.

Middle

image-20240314-062054.png

It is the value of the rebar in the middle region in terms of quantity and diameter. The shearwall mesh reinforced shearwall is written as the mesh rebar type in the cell.

HeadR

image-20240314-062108.png

It is the value of the right area rebar in terms of quantity and diameter.

Stirrup

image-20240314-062138.png

It is the diameter and spacing of the stirrup of the shearwall body region.

Head Stirrup

image-20240314-062151.png

It is the diameter and spacing of the stirrup of the shearwall heading area.

Vd

image-20240314-062204.png

It is the shear force calculated under the combined effect of vertical loads and earthquake loads.

Ve

image-20240314-062221.png

It is the design shear force calculated according to TBDY 7.6.6 and based on the shear transverse reinforcement calculation.

Vr

image-20240314-062236.png

Shearwall shear design strength.

VeMax

image-20240314-062253.png

It is the maximum shear force that the shearwall can take, calculated according to TBDY Equation 7.18.

Cap. Ratio

image-20240314-062309.png

It is the largest of the capacity ratios calculated under the effect of axial force and biaxial bending, under the effect of all combinations in the existing reinforcement layout.

Fiber Layout Tab

image-20240314-062827.png

Specifications

Preview and legend

image-20240314-063157.png

The fiber layout preview and what the colors mean are shown.

Material model for DGT

image-20240314-063212.png

Section cells and rebars are displayed according to the concrete and rebar material model criteria defined in TS500.

Material model for SDGT

image-20240314-063229.png

The section cells and rebars are displayed according to the ŞGDT criteria for the concrete and rebar material model defined in TBDY.

Forces - Reinforcement Areas Tab

image-20240314-063821.png

Specifications

Table of forces

image-20210127-065357.png

Load:  The name of the respective load or load combinations.
i: The left end of the element in the horizontal element is the lower end of the element in the vertical element.
j: The right end of the element in the horizontal element is the upper end of the element in the vertical element.
N: The axial force of the element
V2, V3:  The shear forces of the element in the 2 and 3 directions.
T: The torsion moment of the element.
M2: It is the bending moment of the element in the 2 (minor) direction.
M3: It is the bending moment of the element in the 3 (major) direction.

Reinforcements (calculated - required - existing)

image-20240314-065314.png

Respectively; The area of ​​rebar found from the most unfavorable loading combination, the amount of rebar to be placed according to the regulations and minimum rebar conditions and the total values ​​of the final selected rebar in the left, middle and right regions for the shearwall are given.

Design: It is the name of the combination used in reinforcement calculation.
M3 (major): It  is the moment value in the 3 axis of the combination used in the wall reinforcement calculation.
M2 (minor): It is the moment value in the 2 axis of the combination used in the wall reinforcement calculation.
F1 (axial): It is the normal force value of the combination used in wall reinforcement calculation.

Design results

image-20210126-121055.png

After the analysis, the regulation conditions have been applied, therefore it shows the end forces that have undergone changes and going to the design. In addition, the values ​​used are shown in bold. End forces are values ​​calculated on the element local axes.

Raw results

image-20210126-121111.png

After analysis, it shows the raw end forces that are not applied to the regulation conditions. End forces are effects on the element local axes.

Global results

image-20210126-121126.png

After the analysis, these are the values ​​in global coordinates of the extreme forces that are not applied regulation conditions.

Show individual results

image-20210126-121445.png

For 4 modal analysis cases, 4 different results are obtained from each earthquake loaded combination. If you want the program to display the values ​​obtained for each modal state one by one, you should check this option.

Show maximums

image-20210126-121510.png

The biggest values ​​of 4 different results obtained from each load combination for 4 different modal cases are shown in the table.

Geometric properties

image-20240314-065345.png

hw: The total height of the shearwall throughout the structure.
lw: It is the length value of the shearwall in plan.

Material properties

image-20240314-065907.png

Structural material: The structural material of the shearwall.
fck: The characteristic of concrete is its compressive strength.
fcd: The characteristic calculation of concrete is its compressive strength.
fctd: Characteristic calculation of concrete is its tensile strength.
fyk: It is the yield strength of reinforcement steel.
fyd: It is the calculation strength of reinforcement steel.

Shear force

image-20240314-070343.png

Detailed information on shear force control according to TDY is printed. In walls with high ductility level with Hw / Lw> 2;
And = betav. Vd. Betav = 1.5 as [(Mp) t / (Md) t], but betav = 1.0 is taken for buildings where all earthquake loads are carried by shearwall walls.
hw: The total height of the shearwall throughout the structure.
lw: It is the length value of the shearwall in plan.
(Mp) t: It is the hardened moment capacity value calculated at the base section of the wall.
(Md) t: It is the moment value calculated under the combined effect of vertical loads and earthquake loads multiplied by the load coefficients calculated at the base section of the wall.
Ve:It is the design shear force calculated according to TBDY 7.6.6 and based on the shear transverse reinforcement calculation.
Ve cap value: The shear force obtained by magnifying the shear force calculated from the earthquake with vertical loads by 1.2D or 1.4D times.
Vr: It is the shear strength value of the shearwall section.
And> Vr means that it does not provide cutting safety in the shearwall.
For shearwalls with high ductility level with Hw / Lw <= 2;
And its value is the value calculated from the most unfavorable load combination.
Factor 4.3.4.9: For walls with Hw / Lw <= 2, the end forces are increased by the coefficient [3 / (1 + Hw / Lw)] according to the R coefficient. However, this value is not taken higher than 2.
VeMax:It is the maximum shear force that the shearwall can take, calculated according to TBDY Equation 7.18.

Capacity Design Tab

image-20240314-072818.png

Specifications

Capacity chart

image-20210127-070212.png

Combination: The corresponding combination is shown.
i: The left end of the element in the horizontal element is the lower end of the element in the vertical element.
j: The right end of the element in the horizontal element is the upper end of the element in the vertical element.
N: The axial force of the element
V2, V3:  The shear forces of the element in the 2 and 3 directions.
T: The torsion moment of the element.
M2: It is the bending moment of the element in the 2 (minor) direction.
M3: It is the bending moment of the element in the 3 (major) direction.
Capacity ratio: It shows the ratio of the effect of the element at the i and j ends of the respective loading / combination to its capacity at that loading. If the value is greater than 1, the element is exceeding the maximum capacity.

Existing area of steel

image-20210127-070255.png

The available rebar area values ​​for end i, span, and end j are shown.

Capacity Diagrams Tab

image-20240314-072837.png

Specifications

Bending about 2 axis

image-20210127-070747.png

Bending about 3 axis

image-20210127-070805.png

Material model for DGT

image-20240314-073113.png

Section cells and rebars are displayed according to the concrete and rebar material model criteria defined in TS500.

SDGT - (new structure)

image-20240313-063229.png

The section cells and rebars are displayed according to the ŞGDT (new structure) criteria for the concrete and rebar material model defined in TBDY.

SDGT - (existing str. - limited information)

image-20240313-063446.png

The section cells and rebars are displayed according to the ŞGDT (existing structure - limited information) criteria for the concrete and rebar material model defined in TBDY.

SDGT - (existing str. - comprehensive info)

image-20240313-063457.png

The section cells and rebars are displayed according to the ŞGDT (existing structure - comprehensive information) criteria for the concrete and rebar material model defined in TBDY.

Design case

image-20240314-073649.png

The combination for the capacity diagrams to be examined can be selected from the list.

Moment - Curvature Tab

image-20250113-080000.png

Specifications

Schematic drawing

image-20240314-075653.png

Moment - curvature diagram

image-20240314-075800.png

Use CP curvature = ultimate curvature

image-20250113-070925.png

When this option is selected, the ultimate strain of the concrete and reinforcement material is used to calculate the plastic rotation limit values for performance levels.

Caltrans idealized model

image-20240314-075817.png

If marked, the moment-curvature plot is idealized. It is a moment curvature relationship obtained by drawing a horizontal line that intersects with an inclined line passing over the moment of yield and will equalize the areas between the moment curvature graph.

Stop when a fiber reaches ultimate stress

image-20210126-143253.png

If checked, the graphic ends when the graphic fiber reaches its highest stress.

DGT

image-20240313-071919.png

Section cells and rebars are displayed according to the concrete and rebar material model criteria defined in TS500.

SGDT

image-20250113-080027.png

The section cells and rebars are displayed according to the SGDT criteria for the concrete and rebar material model defined in TBDY.

Point count

image-20210126-143404.png

It is used to determine how many points the moment curvature graph consists of.

Angle

image-20210126-124330.png

It shows the neutral axis angle from which the moment curvature relationship is obtained. It is indicated with a red arrow in the image above.

Axial force

image-20210126-124347.png

It shows under which axial force the moment curvature relationship is drawn.

Compression limit

image-20210127-071155.png

The determined material model is the largest axial pressure force that the section can take in the moment-normal force interaction.

Tension limit

image-20210127-071202.png

The determined material model is the largest axial tensile force that the section can take in the moment-normal force interaction.

View stress/strain contours

image-20210126-124816.png

It shows the stress and strain state in section in color format at each step of the moment curvature relationship.

Generate report

image-20210126-124846.png

Creates a detailed report of moment-curvature.

Equation 7.3 Control Tab

In this tab, detailed information is given about strong column control in the shearwall long direction according to TDY.  

image-20240314-080029.png

Specifications

Control table

image-20240314-080558.png

Major (+): It is the moment of carrying capacity of the bulkheads in the major direction calculated according to the earthquake + direction.
Major (-): It is the moment of carrying capacity of the walls in the major direction calculated according to the earthquake-direction.
Minor (+): It is the moment of carrying power of the walls in the minor direction calculated according to the earthquake + direction.
Minor (-): It is the moment of carrying power of the walls in the minor direction calculated according to the earthquake-direction.
Mra, Mrü: In the long direction of the shearwall, they are the lower and upper bearing strength moments, respectively.
Mri, Mrj: Beams are the left and right bearing strength moments, respectively.

Mr(c): Sum of nominal flexural strengths of shearwalls (Mra, Mrü) framing into the joint, evaluated faces of joint.
1.2Mr(b): 1.2 times the sum of nominal flexural strengths of beams (Mri, Mrj) framing into the joint, evaluated faces of joint.
Note: information about the case where some shearwalls cannot satisfy the requirement of having shearwalls stronger than beams.

image-20210127-071319.png

(Mra + Mrü) Major: For strong column control, it is the sum of the moments of bearing strength in the long direction of the shearwall (in the 3 axis), above and below the shearwall.
1.2 (Mri + Mrj) Major: It is the sum of the moment of bearing strength on the left and right of the beams connected in the shearwall major direction (3 axis) for strong column control.

(Mra + Mrü) Major> 1.2 (Mri + Mrj) Major control is checked. If not, shearwall sizes are increased.

In case of Nd≤ 0.10 Ac fck in both columns joining the node point, or at the nodal points of the top floor of single-storey buildings and multi-storey buildings, or if the shearwall where the beams are stuck working like a column in a weak direction, the above condition is not compulsory.

The bottom line is; Displays whether Nd is greater than 0.1AcFck.

image-20240314-081212.png

Nd: It is the axial force value that makes these moments the smallest in accordance with the direction of the earthquake in the calculation of column bearing force moments.
Ac: It is the gross cross-sectional area value of the column.
fck: It is the characteristic compressive strength value of concrete.

Reinforcement Bars Tab

image-20240314-081256.png

Specifications

3D image

image-20240314-081404.png

Show columns

image-20240314-081420.png

If the option is selected, column rebars are shown on the screen.

Show beams

image-20240314-081433.png

If the option is selected, beam rebars are shown on the screen.

Show shearwalls

image-20240314-081448.png

If the option is selected, shearwall rebar is shown on the screen.

Show longitudinal bars

image-20240314-081504.png

Longitudinal bars of the elements with option marked are shown on the screen.

Show transverse bars

image-20240314-081515.png

The transverse rebars of the elements with options are displayed on the screen.

Show individual colors

image-20240314-081538.png
image-20210126-130430.png

If the option is selected, bars with different diameters are shown in different colors. Which color represents which diameter is on the right of the screen. If the option is off, all of the rebars are shown in red.