Column Pre-Dimensioning
Ac = Reinforced concrete column cross-section area
fcd = Concrete design compressive strength
Nd = Axial force
  • According to TS 500 7.4.1, the cross section width should be minimum 250 mm in rectangular columns and the maximum normal force that the columns can bear under increased loads should meet the condition Nd ≤ 0.9fcdAc .
  • Depending on the chosen slab thickness, the load coverage areas of the columns will be calculated as shown, and the normal forces occurring in the columns under increased vertical loads will be determined.
  • There are 3 types of load areas as shown in the figure below. These calculations will be shown for Type1 only.
At Roof Story:
  • Loads from dead loads to the column;
  1. From the own weight of the slab: 8 m * 8 m * 0.27 m * 25 kN / m 3 = 432 kN
  2. From the coating load: 8 m * 8 m * 4 kN / m 2 = 256 kN
  3. From the column's own weight (assumed 80 * 80): 0.8 m * 0.8 m * 3.5 m * 25 kN / m 3 = 56 kN
Total G = 432 + 256 + 56 = 744 kN
  • From live load: 8 m * 8 m * 1.0 kN / m2 = 64 kN
Q = 64 kN
Office Stories:
  2. From the coating load: 8 m * 8 m * 1.5 kN / m 2 = 96 kN
Total G = 432 + 96 + 56 = 584 kN
  • From live load: 8 m * 8 m * 2.0 kN / m2 = 128 kN
Q = 128 kN
In Basement Stories:
  2. From the coating load: 8 m * 8 m * 0.5 kN / m 2 = 32 kN
  3. From the column's own weight (assumed 80 * 80): 1 m * 1 m * 3.5 m * 25 kN / m 3 = 88 kN
Total G = 432 + 32 + 88 = 552 kN
  • From live load: 8 m * 8 m * 5.0 kN / m2 = 320 kN
Q = 320 kN
Material Information
Selected Column Front Dimensions
Story
Story elevation
G + Q
1.4G + 1.6Q
Ac≥ N 1.4G + 1.6Q /0.9f cd
Front size selected
12th story
43
808
1144
0.05
60/60
11th story
39.5
1520
2166
0.1
60/60
10th story
36
2232
3189
0.15
60/60
9th story
32.5
2944
4211
0.2
60/60
8th story
29
3656
5234
0.25
60/60
7th story
25.5
4368
6256
0.3
80/80
6th story
22
5080
7278
0.35
80/80
5th story
18.5
5792
8301
0.40
80/80
4th story
15
6504
9323
0.44
80/80
3rd story
11.5
7216
10346
0.49
80/80
2nd story
8
7928
11368
0.54
100/100
1st story
4.5
8640
12390
0.69
100/100
Bas. 1
0
9512
13675
0.65
100/100
Bas. 2
-3.5
10384
14960
0.71
100/100
  • In TBDY 2018 7.3.1, the condition that the cross section dimension of the columns with high ductility level with rectangular cross section can not be less than 300 mm is also provided.