Column - Foundation Connection (Stiffened Base Plate) Design
Column-Foundation Connection or Stiffened Base Plate Connection is formed by connecting the base plate welded to the steel column and anchored to the concrete foundation (column). Stiffened base plate design is made automatically according to the Design, Calculation and Construction Principles of Steel Structures (ÇYTHYEDY) (GKT and YDKT) and AISC 360-16 (ASD and LRFD) regulations. In the stiffened base plate connection calculation, bolt, weld and plate controls, geometry controls and strength controls are made automatically in accordance with the steel connection type.
In the calculation of the stiffened base plate connection, the horizontal and vertical bolt distances and the distance between the bolts are controlled under the geometry control. In the strength control, base plate thickness, anchor pulling breakage, anchor rod peeling, anchor rod shearing, plate bolt hole controls are made.
Geometry Checks
Bolt Spacing
s min ≥ 3d
ÇYTHYEDY 13.3.6
s
180 mm
d
24 mm
s =180 mm > smin = 3*24=72 mm
Horizontal Edge Distance
L eh ≥ L e- min
ÇYTHYEDY 13.3.7
L eh
70 mm
L eh ≥ 2d = 2 * 24 = 48 mm conformity check for application
L e- min
32 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance
L ev ≥ L e- min
ÇYTHYEDY 13.3.7
L ev
45 mm
L e- min
32 mm
Strength Checks
Base Plate Thickness (Bearing)
fc
25000 kN/m2
A 1
A 2
qmax
fp(max)
fp(max)
e
e crit
Y
Y
f
le
45 mm
l
m
n
h
650 mm
b
300 mm
N
900 mm
B
500 mm
M
365.17 kNm
P
739.22 kN
F y
355 N/mm2
t req
AISC DG-1-2 nd
3.3.15.a
Required
Available
Ratio
Control
41.11 mm
42 mm
0.979
Base Plate Thickness (Tension)
fc
25000 kN/m2
A 1
A 2
qmax
e
e crit
T
Y
Y
f
x
le
45 mm
m
h
650 mm
N
900 mm
B
500 mm
M
365.17 kNm
P
739.22 kN
F y
355 N/mm2
t req
AISC DG-1-2 nd
3.4.7a
Required
Available
Ratio
Control
15.312 mm
42 mm
0.365
Anchor Rod Tensile Rupture
A b
Fn
750000 kN/m2
Rn
ΦRn
Required
Available
Ratio
Control
32.429 kN
254,469 kN
0.127
Anchor Rod Concrete Pullout
Ψ
1.0
ACI 318M-08 D.5.3.6
N p
ACI 318M-08 (D-15)
A bgr
7401.592 mm2
fc
25000 kN/m2
Rn
ACI 318M-08 (D-14)
ΦRn
Required
Available
Ratio
Control
32.429 kN
1036.222 kN
0.031
Anchor Rod Shear
A b
Fn
Rn
ΦRn
Required
Available
Ratio
Control
9.995 kN
152,681 kN
0.065
Bolt Bearing on Plate
d h
24+2=26 mm
Lc,edge
Rn
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Rn-edge
Rn
ΦRn
Required
Available
Ratio
Control
9.995 kN
568,511 kN
0.018