4-Bolts Stiffened End Plate Connection Design per AISC 358-16 & AISC 360-16
How does ideCAD design four bolts stiffened end plate connection according to AISC 358-16 & AISC 360-16?
  • Four bolts stiffened end plate connection is designed automatically according to the AISC 358-16 and AISC 360-16 by the ideCAD Structural.
Ag: Gross area
An: Net cross-section area
Aw: Cross-section web area
bp = width of end-plate, in. (mm)
g = horizontal distance between bolts, in. (mm)
dh: Bolt hole diameter
nsp: Number of slip planes
L: Connector distance
pb = vertical distance between the inner and outer row of bolts in an eight-bolt stiffened connection, in. (mm)
pfi = vertical distance from the inside of a beam tension flange to the nearest inside bolt row, in. (mm)
pfo = vertical distance from the outside of a beam tension flange to the nearest outside bolt row, in. (mm)
tbf = thickness of beam flange, in. (mm)
Rn: Characteristic strength
Rnt: Characteristic tensile strength
Rnv: Characteristic shear strength
Connection Geometry
GEOMETRY CHECKS
Horizontal Edge Distance
Leh ≥ L e-min
AISC 360-16 J3.4
Leh
72 mm
Leh ≥ 2d = 2 * 30 = 60 mm conformity check for application
Le-min
46 mm
Vertical Edge Distance
Lev ≥ L e-min
AISC 360-16 J3.4
Lev
72 mm
Lev ≥ 2d = 2 * 30 = 60 mm conformity check for application
Le-min
46 mm
Beam Web to End Plate Weld Size
w ≥ wmin
 AISC 360-16
w
7.072 mm
wmin
5 mm
Table J2.4
Stiffener to Beam Flange Weld Size
w ≥ wmin
 AISC 360-16
w
7.072 mm
wmin
5 mm
Table J2.4
Stiffener to End Plate Weld Size
The minimum size welds are checked according to AISC 360-16 Table J2.4
w ≥ wmin
 AISC 360-16
w
7.072 mm
wmin
5 mm
Table J2.4
w ≥ wmin
 AISC 360-16
w
11.315 mm
wmin
6 mm
Table J2.4
w ≥ wmin
 AISC 360-16
w
11.315 mm
wmin
6 mm
Table J2.4
Prequalification Limits (AISC 358-16 Table 6.1)
All end-plate moment connection configurations should satisfy these beam and column limitations. Beam and column limitations are given in AISC 358-16 Table 6.1.
Beam span / Beam cross-section height
9144 mm /450 mm=20.32
≥7.0
End plate thickness, tp
32 mm
13≤tp ≤38
End plate width, bp
290 mm
178≤ bp ≤ 273
Horizontal distance between bolts, g
150 mm
83≤g≤152
pfi
60 mm
44≤pfi ≤140
pfo
60 mm
44≤pfo ≤140
Beam depth, db
450 mm
349≤db≤610
Beam flange thickness, tbf
15 mm
10≤tbf ≤19
Beam flange width, bbf
190
152≤bbf ≤229
Column depth
650
≤ 920 mm
Bolt grade
10.9
8.8 - 10.9
Min yield stress of the end plate material
275 MPa
235 /275 / 355 MPa
Flange plate weld
CJP
CJP
STRENGTH CHECKS
Bolt diameter
The required bolt diameter, db, for four bolts stiffened end plate connection is checked according to AISC 358-16 §6.8
Muc
821.813 kNm
AISC 358-16 (6.8-3)
Ft
750000 kN/m2
ho
h1
db
Required
Available
Ratio
Control
29.825 mm
36 mm
0.829
End Plate Thickness
The required end plate thickness, tp, for four bolts stiffened end plate connection is checked according to AISC 358-16 §6.8
Muc
821.813kNm
AISC 358-16 (6.8-5)
Fyp
275000 kN/m2
s
Yp
Yp
tp
Required
Available
Ratio
Control
27.327 mm
30 mm
0.911
End Plate Stiffener Thickness
The required stiffener thickness, tb, for four bolts stiffened end plate connection is checked according to AISC 358-16 §6.8
tbw
9 mm
AISC 358-16 (6.8-9)
Fyb
275000 kN/m2
Fys
275000 kN/m2
ts
12 mm
Required
Available
Ratio
Control
9 mm
12 mm
0.750
End Plate Stiffener Local Buckling
Stiffener local buckling limit state for four bolts stiffened end plate connection is checked according to AISC 358-16 §6.8
hs
144 mm
AISC 358-16 (6.8-10)
ts
12 mm
E
200000000 kN/m2
Fys
275000 kN/m2
Required
Available
Ratio
Control
12
15.102
0.795
The required end weld size for four bolts stiffened end plate connection is checked.
Fys
275000 kN/m2
AISC DG 4-2 nd
3.2.10
ts
12 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
6.35
7.072
0.898
Fys
275000 kN/m2
AISC DG 4-2 nd
3.2.10
ts
12 mm
Fe
490000 kN/m2
w
Required
Available
Ratio
Control
6.35
7.072
0.898
Bolt Shear Check
The shear limit state of end plate bolts is checked according to AISC 360-16.
Ab
AISC 358-16 6.8.11
Fn
Rn
ΦRn
Required
Available
Ratio
Control
271.371 kN
1648.959 kN
0.165
Bolt Bearing on End Plate
Bearing strength limit states of the connection plate that are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts are checked according to AISC 360-16.
dh
36+3=39 mm
Lc,edge
Rn
AISC 358-16 6.8-12
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
271.371 kN
3307.716 kN
0.082
Bolt Bearing on Column Flange
db
36 mm
Rn
AISC 358-16 6.8-12
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
271.371 kN
3953.318 kN
0.069
The required end weld size for four bolts stiffened end plate connection is checked according to AISC 358-16 §6.7
Fyp
275000 kN/m2
AISC 358-16
(6.7.6) 3
tbw
9 mm
F e
490000 kN/m2
w
Required
Available
Ratio
Control
4.763 mm
7.072 mm
0.673
Column Flange Thickness
The required column flange thickness, tcf, for four bolts unstiffened end plate connection is checked according to AISC 358-16 §6.8
Muc
821.813 kNm
AISC 358-16 (6.8-13)
Fyp
275 N/mm2
s
c
Yc
Yc
tcf
Required
Available
Ratio
Control
25.618 mm
31 mm
0.826
Column Panel Zone Shear
Yielding of the column panel zone for four bolts unstiffened end plate connection is checked according to AISC 360-16 §J.10
Pr
355.597 kN
AISC 360-16 J10-9
Py
Fy
275000 kN/m2
Ag
28634.759 mm2
dc
650 mm
tw
16 mm
Rn
ΦRn
Required
Available
Ratio
Control
1673.526 kN
1716 kN
0.975
Panel Zone Thickness
The required panel zone thickness for four bolts unstiffened end plate connection is checked according to AISC 358-16.
tmin≥u/180
t min = tw
16 mm
tw
16 mm
u
2016 mm
Required
Available
Ratio
Control
11.2 mm
16 mm
0.700