Shear Wall Required and Design Strength per ACI 318-19 with ideCAD
How does ideCAD concrete shear wall required, and design strength according to ACI 318-19?
  • Wall required strengths are calculated automatically.
  • Wall design strengths are calculated automatically.
:check_mark:
Notation
D = dead load
E = earthquake load
L = live load
Lr = roof live load
R = rain load
S = snow load
U = strength of a member or cross section required to resist factored loads or related internal moments and forces in such combinations as stipulated in ACI 318-19
W = wind load
ϕ = strength reduction factor
Required Strength
The required strength is calculated in accordance with the factored load combinations in Load Factors and Combinations per ACI 318-19 with ideCAD title.
Reinforced concrete walls with rectangular, I, T, L, U, or C crosssections are modeled with finite elements (shells) containing degrees of freedom for both in-plane and out-of-plane displacements. The resultant of the finite element joint forces are obtained as equivalent internal force (Mu, Pu) at the cross-section gravity center, based on shear wall required strength and design strength calculations.
The wall shear design is applied leg by leg for each design load combination. The factored shear force, Vu of the leg, is determined and compared with the design shear strength ϕVn.
Design Strength
Design strength in all sections should satisfy all conditions given below;
  • ϕPn ≥ Pu
  • ϕMn ≥ Mu
  • ϕVn ≥ Vu
Strength reduction factors ϕ is determined according to using ACI Table 21.2.2. Interaction between load effects is considered.
Strain, εt
Section Classification
ϕ
εt ≤ εty
Compression Controlled Moment
0.65
εty < εt < (εty + 0.003)
Transition region
0.65 + 0.25[(εt - εty)/0.003]
εt ≥ (εty + 0.003)
0.90
Pn and Mn are calculated in accordance with Axial strength or Combined Flexural and Axial Strength per ACI 318-19 with ideCAD title.
:check_mark: