Transverse Reinforcement (SwRD) per ACI 318-19 with ideCAD
How does ideCAD control shear wall transverse reinforcement detailing according to ACI 318-19?
  • Transverse reinforcement detailing is applied automatically in accordance with ACI 11.7
  • Transverse reinforcement detailing is applied according to ACI Chapter 18 in special structural walls.
:check_mark:
Notation
Acv = gross area of concrete section bounded by web thickness and length of section in the direction of shear force considered in the case of walls, and gross area of concrete section in the case of diaphrams. Gross area is total area of defined section minus area of any openings, in.2
Acw = area of concrete section of an individual pier, horizontal wall segment, or coupling beam resisting shear, in2.
ϕ = strength reduction factor
According to ACI 11.7.3.1, the maximum spacing of transverse reinforcement bars in shear walls is the lesser of 3h and 18 inches. If shear reinforcement is required for in-plane strength, the maximum s should be lw/5.
According to ACI 11.7.4.1, longitudinal reinforcement should be laterally supported by transverse reinforcement if the following two conditions are satisfied;
  • Ast > 0.01Ag
  • longitudinal reinforcement is required
Earthquake-Resistant Structures
Special structural walls
According to ACI 18.10.4.3, shear walls should have distributed shear reinforcement in two orthogonal directions in the plane of the wall. If hw/lw ≤ 2.0, the reinforcement ratio ρl should be at least the reinforcement ratio ρt.
:check_mark: