Brace Center Connection Design
The brace center connection is formed by bolting and welding the steel brace member to the column, beam or column-to-beam connection point by bolting and welding. Bolt control, weld control, plate control and connection application limits control are performed automatically according to the placement of the elements of the connection. Brace center connection design is made automatically according to the Design, Calculation and Construction Principles of Steel Structures (ÇYTHYEDY) or AISC 360-16 regulations and a connection report is created.
In the brace center connection calculation, horizontal and vertical bolt distances, butt plate weld thickness, continuity plate weld thickness and application limits are checked under geometry control. In strength control, cross bolt slip, plate bolt hole crushing, ski control, Whitmore section buckling, plate pressure leakage are checked.
Connection Geometry
Brace - Gusset Connection
Geometry Checks
Bolt Spacing
s min ≥ 3d
ÇYTHYEDY 13.3.6
s
60 mm
d
20 mm
s =60 mm > smin = 3*20=60 mm
Horizontal Edge Distance
L eh ≥ L e- min
ÇYTHYEDY 13.3.7
L eh
57 mm
L e- min
26 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance
L ev ≥ L e- min
ÇYTHYEDY 13.3.7
L ev
45 mm
Conformity check for L eh ≥ 2d = 2 * 20 = 40 mm application
L e- min
26 mm
Weld Size
a ≥ a min
ÇYTHYEDY 13.3.7
a
4 mm
a min
3.5 mm
Table 13.4
Strength Checks
Bolt Shear at Brace
A b
Fn
Rn
ΦRn
Required
Available
Ratio
Control
169.593 kN
212.058 kN
0.800
Bolt Bearing on Plate
d h
20+2=22 mm
Lc,edge
Rn
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
169.593 kN
456.84 kN
0.371
Bolt Bearing on Gusset
d h
20+2=22 mm
Lc,edge
Rn
ÇYTHYEDY 13.3.13
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
169.593 kN
304.56 kN
0.557
Weld Strength
Fe
490000 kN/m2
w
The weld thickness taken from the combination menu is 0.707 * w value. 4 / 0.707 = 5.658 mm
F u-plate
469.999  N/mm2
F u-brace
410 N/mm2
tplate
15 mm
t brace
15 mm
lw
150 mm
R nw
Rn-plate
Rn-brace
RnBM
Rn
ΦRn
Required
Available
Ratio
Control
169.593 kN
529.2 kN
0.320
Whitmore Section Compression Yield
K
0.65
L
0 mm
r
2.887 mm
KL / r
0
Fy
355 N/mm2
Ag
1292.82 mm2
Rn
ÇYTHYEDY 13.20
ΦRn
Required
Available
Ratio
Control
169.593 kN
413,056 kN
0.411
Gusset Compression Yield
K
0.65
L
65 mm
r
4.33 mm
KL / r
9.76
Fy
355 N/mm2
Ag
2009.999 mm2
Rn
ÇYTHYEDY 13.20
ΦRn
Required
Available
Ratio
Control
169.593 kN
642,195 kN
0.264