How does ideCAD control column reinforcement limits according to ACI 318-19?
Longitudinal and Transverse reinforcement limits are controlled automatically.
Ach = cross-sectional area of a member measured to the outside edges of transverse reinforcement, in.2
Ash = total cross-sectional area of transverse reinforcement, including crossties, within spacing s and perpendicular to dimension bc, in.2
Av,min = minimum area of shear reinforcement within spacing s, in.2
bc = cross-sectional dimension of member core measured to the outside edges of the transverse reinforcement composing area Ash, in.
db = nominal diameter of bar, wire, or prestressing strand, in.
hx = maximum center-to-center spacing of longitudinal bars laterally supported by corners of crossties or hoop legs around the perimeter of a column or wall boundary element, in.
kf = concrete strength factor
kn = confinement effectiveness factor
lo = length, measured from joint face along axis of member, over which special transverse reinforcement must be provided, in.
nl = number of longitudinal bars around the perimeter of a column core with rectilinear hoops that are laterally supported by the corner of hoops or by seismic hooks.
so = center-to-center spacing of transverse reinforcement within the length lo, in.
ϕ = strength reduction factor
ρs = ratio of volume of spiral reinforcement to the total volume of core confined by the spiral, measured out-to-out of spirals
The transverse reinforcement area is applied to provide the equation ϕVn ≥ Vu, described in Column Shear Design per ACI 318-19 with ideCAD title for all columns.
Minimum and maximum longitudinal reinforcement
For nonprestressed columns,
minimum longitudinal reinforcement area is 0.01Ag
maximum longitudinal reinforcement area is 0.08Ag.
Minimum shear reinforcement
A minimum area of shear reinforcement, (Av)min should be provided in all sections where Vu > 0.5ϕVc.
According to ACI 10.6.2.2; If shear reinforcement is required, Av,min is equal to the greater of the following relations;
Columns of Earthquake-Resistant Structures
Ordinary moment frames
All of the reinforcement limits described above are valid for columns of ordinary moment frames.
Intermediate moment frames
Special moment frames
For columns of special moment frames,
maximum longitudinal reinforcement area is 0.06Ag.
Over column clear height, longitudinal reinforcement shall be selected such that 1.25ld≤lu/2.
Spacing of transverse reinforcement shall not exceed the least of conditions give below;
One-fourth of the minimum column dimension
For Grade 60 or S420, 6db of the smallest longitudinal bar
For Grade 80, 5db of the smallest longitudinal bar
so, as calculated by: (The value of so shall not exceed 6 in. and need not be taken less than 4 in.)
The amount of transverse reinforcement is in accordance with ACI Table 18.7.5.4.
Transverse Reinforcement Area |
Conditions |
Applicable expressions |
Ash for rectengular hoop |
Maximum value of (a) and (b) |
Maximum value of (a), (b), and (c) |
ρs for spiral or cicular hoop |
Maximum value of (d and (e) |
Maximum value of (d), (e), and (f) |
The concrete strength factor kf and confinement effectiveness factor kn are calculated as given below;