Joining Plates Connection
The joining plates connection is a moment transmitting connection formed by connecting the end plates welded to two beams with bolts. Bolt control, welding control, plate control are made automatically according to the placement of the elements of the connection. The connection design of the joining plates connection is made automatically according to the Design, Calculation and Construction Principles of Steel Structures (ÇYTHYEDY) or AISC 360-16 regulations and the connection report is created.
In the calculation of the joining plates connection, the distance between the bolts, the horizontal and vertical edge distance of the bolts and the weld thickness are checked under geometry control. In the strength control, tension in the support bolts, thickness of the end plate, shear yield of the end plate, shear failure of the end plate, slip on the support bolts, crushing of the bolt hole in the end plate and weld strength are checked.
Connection Geometry
Geometry Checks
Horizontal Edge Distance
L eh ≥ L e- min
ÇYTHYEDY 13.3.7
L eh
55 mm
L eh ≥ 2d = 2 * 24 = 48 mm conformity check for application
L e- min
32 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance
L ev ≥ L e- min
ÇYTHYEDY 13.3.7
L ev
51.515 mm
L e- min
32 mm
Weld Size 1
a ≥ a min
ÇYTHYEDY 13.3.7
a
6 mm
a min
3.5 mm
Table 13.4
Strength Checks
Bolt Tension at Support
Ft
750000 kN/m2
Ab
AISC DG-4-2 nd
3.7
Pt
h0
x1
314.368 mm
dm
393.235 mm
Mreq
40.179 kNm
Nreq
16,552 kN
Rreq
Rn
ΦRn
Required
Available
Ratio
Control
93.899 kN
1017.876 kN
0.092
End Plate Thickness
A b
P t
M n
AISC 358-16 (6.8-5)
F yp
235346 kN/m2
Y p
2510.75 mm
t p
Required
Available
Ratio
Control
28.903 mm
30 mm
0.963
End Plate Shear Yield
F yp
235359 kN/m2
A g
ÇYTHYEDY 13.17
dm
393.235 mm
M req
40.179 kNm
N req
16.552 kN
R req
Rn
ΦRn
Required
Available
Ratio
Control
93.899 kN
1779.31 kN
0.053
End Plate Shear Rupture
F u
362846 kN/m2
To u
ÇYTHYEDY 13.18
dm
393.235 mm
M req
40.179 kNm
N req
16.552 kN
R req
Rn
ΦRn
Required
Available
Ratio
Control
93.899 kN
1508.714 kN
0.062
Bolt Shear at Support
A b
Fnv
Rn
ÇYTHYEDY 13.10b
ΦRn
Required
Available
Ratio
Control
1,058 kN
610,725 kN
0.002
Bolt Bearing on End Plate
d h
24+2=26 mm
Lc,edge
Rn
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
1,058 kN
1695.14 kN
0.001
Weld Size 1
F yp
235359 kN/m2
AISC DG-4-2 nd
2.1.7
tbw
9 mm
F e
480000 kN/m2
in
Required
Available
Ratio
Control
3.976 mm
8.487 mm
0.469
Weld Strength 1
in
8.487 mm
F E
480 N/mm2
the e
189.75 mm
Rn
AISC DG-4-2 nd
2.1.8
R n / Ω
Required
Available
Ratio
Control
1,058 kN
491.8 kN
0.002