Brace-Corner Connection Design per AISC 360-16
How does ideCAD design brace-corner connection according to AISC 360-16?
  • Brace-corner connection design limit states and geometry checks are done automatically according to AISC 360-16.
  • Brace-corner connection compressive buckling in the withmore section of the plate checks are done automatically according to AISC 360-16.
Ag: Gross area
An: Net cross-section area
d: Characteristic diameter of the stem of the bolt (the diameter of the non-threaded stem of the bolt)
dh: Bolt hole diameter
t: Plate thickness
w = Size of weld leg, in. (mm)
Rn: Characteristic strength
Ubs: A coefficient considering the spread of tensile stresses
Connection Geometry
Brace to Gusset Plate Connection
GEOMETRY CHECKS
Bolts Spacing
The distance between the centers of bolts is checked per AISC 360-16.
smin ≥ 3d
AISC 360-16 J3.3
s
60 mm
d
20 mm
s =60 mm > smin = 3*20=60 mm
Horizontal Edge Distance
Leh ≥ Le-min
AISC 360-16 J3.4
Leh
39.85 mm
Le-min
26 mm
Vertical Edge Distance
Lev ≥ Le-min
AISC 360-16 J3.4
Lev
40 mm
Conformity check for L eh ≥ 2d = 2 * 20 = 40 mm application
Le- min
26 mm
Weld Size
w ≥ wmin
AISC 360-16 J2.4
w
5.658 mm
wmin
5 mm
Table J2.4
STRENGTH CHECKS
Bolt Shear at Brace
The bolt shear limit state of the connection is checked according to AISC 360-16.
Ab
Fn
Rn
AISC 360-16 J3-1
ΦRn
Required
Available
Ratio
Control
413.063 kN
424.115 kN
0.974
Bolt Bearing on Plate
The bearing strength limit states of the connection plate, which are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts, are checked according to AISC 360-16.
dh
20+2=22 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
413.063 kN
906.912 kN
0.455
Bolt Bearing on Gusset
dh
20+2=22 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Available
Ratio
Control
413.063 kN
566.82 kN
0.729
Weld Strength
The nominal and design strength of the weld is checked according to AISC 360-16
Fe
490000 kN/m2
w
5.658 mm
Fu-plate
469.999  N/mm2
Fu-brace
410 N/mm2
tplate
16 mm
tbrace
10 mm
Rnw
Rn-plate
Rn-brace
RnBM
Rn
ΦRn
Required
Available
Ratio
Control
413.063 kN
493.92 kN
0.836
Whitmore Section Buckling
The buckling limit state in withmore section of the plate subjected to compression is checked according to AISC 360-16.
K
0.65
L
159.85 mm
r
2.887 mm
KL / r
35.99
Fy
355 N/mm2
Ag
1892.82 mm2
Fe
AISC 360-16 E3-4
Fcr
AISC 360-16 E3-2
Rn
 AISC 360-16 E3-1
ΦRn
Required
Available
Ratio
Control
413.063 kN
548.567 kN
0.753
Plate Compression Yield
The yield limit state of the connection plate subjected to compression is checked according to AISC 360-16.
K
0.65
L
60 mm
r
4.619 mm
KL / r
8.44
Fy
355 N/mm2
Ag
3195.199 mm2
Rn
AISC 360-16 J4-6
ΦRn
Required
Available
Ratio
Control
413.063 kN
1020.866 kN
0.405
Gusset-to-Support Connection
GEOMETRY CHECKS
Weld Size
w ≥ wmin
w
4 mm
wmin
3.5 mm
Table J2.4
STRENGTH CHECKS
Gusset Axial Yield
The yield limit state of the connection gusset plate subjected to axial force is checked according to AISC 360-16.
Fy
355 N/mm2
Zg
Fa
N
260,207 kN
M
10.775 kNm
tg
10 mm
lg
365.24 mm
Fb
Fn
Rn
ΦRn
Required
Available
Ratio
Control
116237.092 kN/m2
319500 kN/m2
0.364
Gusset Shear Yield
Fy
355 N/mm2
V
292.079 kN
tg
10 mm
lg
365.24 mm
Fv
Rn
ΦRn
Required
Available
Ratio
Control
79969.139 kN/m2
213000 kN/m2
0.375
Weld Strength
Fpeak
Favg
Rreq
AISC 360-16 J2-4
tg
10 mm
w
5.658 mm
Fe
490000 kN/m2
θ
55.473 °
Rn
ΦRn
Required
Available
Ratio
Control
1451.376 kN/m
2423.547 kN/m
0.599