How does ideCAD control column transverse reinforcement detailing according to ACI 318-19?
Transverse reinforcement detailing is applied automatically in accordance with ACI 10.7.6
Transverse reinforcement detailing is applied according to ACI Chapter 18 in earthquake resistant structure columns.
Notation
Ag = gross area of concrete section, in.2 For a hollow section, Ag is the area of the concrete only and does not include the area of the void(s)
Ab = area of an individual bar or wire, in.2
hx = maximum center-to-center spacing of longitudinal bars laterally supported by corners of crossties or hoop legs around the perimeter of a column or wall boundary element, in.
lo = length, measured from joint face along axis of member, over which special transverse reinforcement must be provided, in.
so = center-to-center spacing of transverse reinforcement within the length lo, in.
The spacing of transverse reinforcement is determined automatically to meet the most restrictive requirements. The detail of transverse reinforcements is in accordance with Transverse Reinforcement per ACI 318-19 with ideCAD title. The conditions given in the heading Transverse Reinforcement per ACI 318-19 with ideCAD for column gives are given below.
Column Ties
Ties apply a closed loop of the deformed bar, and satisfy the rules:
Center-to-center spacing does not exceed at least 16db of the longitudinal bar.
The minimum diameter of the tie bar is controlled automatically according to ACI 25.7.2.2. The diameter of the tie bar is at least:
No. 3 enclosing No.10 or smaller longitudinal bars
No. 4 enclosing No.11 or larger longitudinal bars or bundled longitudinal bars
Rectilinear ties are arranged to satisfy the conditions given below:
Every corner and alternate longitudinal bar have lateral support provided by the corner of a tie with an included angle of not more than 135 degrees
No unsupported bar is farther than 6 in. clear on each side along the tie from a laterally supported bar
Lateral support of longitudinal bars using ties, hoops, and spirals
In any story, the bottom tie or hoop above the top of the footing or slab can be located at most half the distance of the tie or hoop spacing. Similarly, in any story, the top tie or hoop below the lowest horizontal reinforcement int he slab, drop panel, or shear cap can be located at most half the distance of tie or hoop spacing. (ACI 10.7.6.2)
In any story, the bottom of the spiral should be located at the top of the footing or slab. The top of the spiral should be located in accordance with ACI Table 10.7.6.3.2.
In cases where longitudinal bars are offset, horizontal support should be provided by ties, hoops, spirals, or parts of the floor construction should also be designed to resist 1.5 times the horizontal component of the calculated force in the inclined portion of the offset bar (ACI 10.7.6.4).
According to ACI 10.7.6.4.2, Transverse reinforcement should be placed not more than 6 in. from points of the bend.
The maximum spacing of shear reinforcement for nonprestressed columns is given ACI Table 10.7.6.5.2.
Vs |
Maximum s, in. |
Columns of Earthquake-Resistant Structures
Ordinary moment frames
All the transverse reinforcement detailing conditions described above are applied to columns of ordinary moment frames.
Intermediate moment frames
All the transverse reinforcement detailing conditions described above are applied to columns of intermediate moment frames.
According to ACI 18.4.3.3, at the top and bottom ends of the column, hoops should be provided at spacing along a length measured from the joint face.
Spacing so should not be greater than all of the tree conditions given below.
For Grade 60 or S420, the smaller 8db of the smallest longitudinal bar is enclosed and 8 in.
For Grade 80, the smaller 6db of the smallest longitudinal bar is enclosed and 6 in.
One-half of the smallest cross-sectional dimension of the column.
Length lo should be greater than the maximum of conditions given below.
One-sixth of the clear span of the column
The maximum cross-sectional dimension of the column
18 in.
According to ACI 18.4.3.4, the maximum distance between the first hoop and the joint face is so/2.
ACI 18.4.3.6 states that, Columns supporting reactions from discontinuous stiff members, such as walls, should be provided with transverse reinforcement at the spacing so in accordance with ACI 18.4.3.3 over the full height beneath the level at which the discontinuity occurs if the portion of factored axial compressive force in these members related to earthquake effects exceeds Agfc′/10. If design forces have been magnified to account for the overstrength of the vertical elements of the seismic-force-resisting system, the limit of Agfc′/10 should be increased to Agfc′/4. Transverse reinforcement shall extend above and below the column in accordance with ACI 18.7.5.6(b).
Special moment frames
All the transverse reinforcement detailing conditions described above are applied to columns of special moment frames.
According to ACI 18.7.5.1, Length lo should be greater than the maximum of conditions given below.
The depth of the column at the joint face or at the section where flexural yielding is likely to occur
18 in.
The transverse reinforcement should satisfy all the conditions below along the length lo from each joint face and on both sides of any section where flexural yielding is likely to occur due to lateral displacements beyond the elastic range of behavior. According to ACI 18.7.5.2, transverse reinforcement should be in accordance with the following,
Transverse reinforcement should consist of single or overlapping spirals, circular hoops, or single or overlapping rectilinear hoops with or without crossties.
Bends of rectilinear hoops and crossties should engage peripheral longitudinal reinforcing bars.
Provided that ACI 25.7.2.2 limits are met, the crossover size may be equal to or smaller than the stirrup bar size. Consecutive crossties should be alternated end for end along the longitudinal reinforcement and around the perimeter of the cross-section.
Where rectilinear hoops or crossties are used, they shall provide lateral support to longitudinal reinforcement in accordance with ACI 25.7.2.2 and ACI 25.7.2.3.
While arranging the reinforcement, the spacing of longitudinal bars laterally supported by the corner of a crosstie or hoop leg, hx, will not exceed 14 in. around the perimeter of the column.
Where Pu>0.3Agfc' or fc'>10,000 in columns with rectilinear hoops, every longitudinal bar or bundle of bars around the perimeter of the column core should have lateral support provided by the corner of a hoop or by a seismic hook, and hx smaller than 8 in.
According to ACI 18.7.5.3, the maximum spacing of transverse reinforcement should be the least of the conditions given below;
One-fourth of the minimum column dimension
For Grade 60 or S420, 6db of the smallest longitudinal bar
For Grade 80, 5db of the smallest longitudinal bar
so, as calculated by using ACI Eq. (18.7.5.3); (The value of so shall not exceed 6 in. and need not be taken less than 4 in.)
According to ACI 18.7.5.5, beyond the length lo, the conditions given below should be satisfied;
The column should contain spiral reinforcement column shall contain spiral reinforcement in accordance with ACI 25.7.3 or hoop, and crosstie reinforcement should satisfy ACI 25.7.2 and ACI 25.7.4, with spacing s no more than 6 in.
According to ACI 18.7.5.6, columns supporting reaction from discontinued stiff members, such as walls, should satisfy two conditions below;
If the factored axial compressive force, Pu, of these columns, is greater than Agfc′/10, transverse reinforcement required by ACI 18.7.5.2, 18.7.5.3, and 18.7.5.4 should be provided over the full height at all levels beneath the discontinuity. The limit of Agfc′/10 shall be increased to Agfc′/4, if design forces have been magnified to account for the overstrength of the vertical element of the earthquake resistance structure.
Where ld is in accordance with ACI 18.8.5., transverse reinforcement shall extend into the discontinued member at least ld of the largest longitudinal column bar. Where the lower end of the column terminates on a wall, the required transverse reinforcement should extend into the wall at least ld of the largest longitudinal column bar at the point of termination. If the column terminates on a footing or mat, the required transverse reinforcement will extend at least 12 inches into the footing or mat.
According to ACI 18.7.5.7, if the concrete cover outside the confining transverse reinforcement is greater than 4 in., additional transverse reinforcement having cover not exceeding 4 in. and spacing not exceeding 12 in. should be provided.
According to ACI 18.7.6.2.1, if both conditions are given below, transverse reinforcement over the lengths lo should be designed to resist shear, assuming Vc=0.
The earthquake-induced shear force, calculated in accordance with ACI 18.7.6.1, is at least one-half of the maximum required shear strength within lo.
The factored axial compressive force Pu including earthquake effects, is less than Agfc′/10.