How does ideCAD calculate development length according to ACI 318-19?
The √FC values used to calculate development length should not exceed 100 psi. This is automatically controlled according to 25.4.1.4.
For deformed bars or deformed wires, ld is calculated automatically by Table 25.4.2.3.
ψe = factor used to modify development length based on reinforcement coating
ψg = factor used to modify development length based on the grade of reinforcement
ψs = factor used to modify development length based on reinforcement size
ψt = factor used to modify development length for casting location in tension
λ = modification factor to reflect the reduced mechanical properties of lightweight concrete relative to normal-weight concrete of the same compressive strength
Ktr = transverse reinforcement index, in.
Atr = total cross-sectional area of all transverse reinforcement within spacing s that crosses the potential plane of splitting through the reinforcement being developed, in.2
f'c = specified comprehensive strength of concrete, psi
fy = specified yield strength of non-prestressed reinforcement, psi
ld = development length in tension of deformed bar, deformed wire, plain and deformed welded wire reinforcement, or pretensioned strand.
s = center-to-center spacing of items, such as longitudinal reinforcement, transverse reinforcement, tendons, or anchors.
Development of reinforcement
The fact embedment length should adopt determined tension or compression in reinforcement at each member section; hook, head deformed bar, mechanical device, or a combination according to 25.4.1.
Heads and hooks should not be used to develop bars in compression, according to 25.4.1.2.
The √fc values used to calculate development length should not exceed 100 psi. It’s automatically controlled according to 25.4.1.4.
Development of deformed bars and deformed wires in tension
Development length ld for deformed bars and deformed wires in tension is controlled the greater of below:
Length calculated in accordance with 25.4.2.3 or 25.4.2.4 using the applicable modification factors of 25.4.2.5
12 in
For deformed bars or deformed wires, ld is calculated in accordance with Table 25.4.2.3.
Spacing and cover |
#6 and smaller bars |
#7 and larger bars |
Clear spacing of bars or wires
Other Cases |
All modification factors for developing deformed bars and wires are chosen automatically according to Table 25.4.2.5.
Modification factor |
Condition |
Value of factor |
Lightweight concrete |
0.75 |
Normalweight concrete |
1.0 |
Reinforcement grade, ψg |
Grade 40 or Grade 60 |
1.0 |
Grade 80 |
1.15 |
Grade 100 |
1.3 |
Epoxy ψe |
Epoxy-coated or zinc and epoxy dualcoated reinforcement with clear cover less than 3db or clear spacing less than 6db |
1.5 |
Epoxy-coated or zinc and epoxy dual-coated reinforcement for all other conditions |
1.2 |
Uncoated or zinc-coated (galvanized) reinforcement |
1.0 |
No. 7 and larger bars |
1.0 |
No. 6 and smaller bars and deformed wires |
0.8 |
More than 12 in. of fresh concrete placed below horizontal reinforcement |
1.3 |
Other |
1.0 |
Alternatively, ld can be calculated with Eq. 25.4.2.4a and 25.4.2.4b.
(cb + Ktr)/db is not exceeded 2.5,
Where n is the number of bars, wires being developed, or lap spliced along the splitting plane, it is permitted to use Ktr = 0 reinforcement is present or required.
When Eq. 25.4.2.4a is calculated with the prerequisite (cb + Ktr)/db = 2.5 is used with the development length can be determined as less than calculated according to Table 25.4.2.3.
Development of standard hooks in tension
Development length ldh for deformed bars in tension terminating in a standard hook is the greater of
8db
6 in.
25.4.3.3 The total cross-sectional area of ties or stirrups confining hooked bars Ath shall consist of (a) or (b):
(a) Ties or stirrups that enclose the hook and satisfy 25.3.2.
(b) Other reinforcement enclosing the hook, that extends at least 0.75dh from the enclosed hook in the direction of the bar in tension, and is in accordance with (1) or (2).
For members with confining reinforcement that is both parallel and perpendicular to ldh, it shall be permitted to use the value of Ath based on (1) or (2) that results in the lower value of ldh.
(1) Two or more ties or stirrups shall be provided parallel to ldh enclosing the hooks, evenly distributed with a center-to-center spacing not exceeding 8db, and within 15db of the centerline of the straight portion of the hooked bars, where db is the nominal diameter of the hooked bar.
(2) Two or more ties or stirrups shall be provided perpendicular to ldh, enclosing the hooked bars, and evenly distributed along ldh with a center-to-center spacing not exceeding 8db, where db is the nominal diameter of the hooked bar.
According to 25.4.3.4, for bars being developed by a standard hook at discontinuous ends of members with both side cover and top (or bottom) less than 2-1/2 in., the rules below should be supplied:
The hook is enclosed along ldh within ties or stirrups perpendicular to ldh at s≤3db
The first tie or stirrup encloses the bent portion of the hook within 2db of the outside of the bend
25.4.9 - Development of deformed bars and deformed wires in compression
Development length ldc for deformed bars and deformed wires in compression is greater of
- Length calculated in accordance with 25.4.9.2
- 8 in.
According to 25.4.9.2, ldc is the greater of (a) and (b), using the modification factors in Table 25.4.9.3
ψr is permitted to be taken as 1.0.