Column Required and Design Strength per ACI 318-19 with ideCAD
How does ideCAD calculate concrete column required, and design strength according to ACI 318-19?
  • Column required strengths are calculated automatically.
  • Column design strengths are calculated automatically.
:check_mark:
Notation
D = dead load
E = earthquake load
L = live load
Lr = roof live load
R = rain load
S = snow load
U = strength of a member or cross section required to resist factored loads or related internal moments and forces in such combinations as stipulated in ACI 318-19
W = wind load
ϕ = strength reduction factor
Required Strength
The required strength is calculated in accordance with the factored load combinations in Load Factors and Combinations per ACI 318-19 with ideCAD title. Combined Axial and Flexural Required strengths of a column Pu and Mu occur simultaneously for a column. Therefore, for each applicable factor load combination specified in ACI Table 5.3.1, the most unfavorable condition of Pu and Mu occurring simultaneously is considered.
Design Strength
Design strength in all sections should satisfy all conditions given below;
  • ϕPn ≥ Pu
  • ϕMn ≥ Mu
  • ϕVn ≥ Vu
  • ϕTn ≥ Tu
Strength reduction factors ϕ is determined according to using ACI Table 21.2.2. Interaction between load effects is considered.
Strain, εt
Section Classification
ϕ
εt ≤ εty
Compression Controlled Moment
0.65
εty < εt < (εty + 0.003)
Transition region
0.65 + 0.25[(εt - εty)/0.003]
εt ≥ (εty + 0.003)
0.90
Pn and Mn is calculated in accordance with Axial strength or Combined Flexural and Axial Strength per ACI 318-19 with ideCAD title. Combined Axial and Flexural strengths create a three-dimensional interaction failure surface. In addition to axial compression and biaxial bending, the formulation allows for axial tension and biaxial bending considerations. An interaction surface of a column is shown below.
:check_mark: