Welded Web Connection Design
Welded Web Connection is formed by joining column cap - beam cap with full penetration butt weld, column cap - beam body with welded and bolted plate. Body plate bolt control, welding control, plate control and connection application limits control are made automatically according to the placement of the elements of the connection. Welded Web Connection design is made automatically according to the Design, Calculation and Construction Principles of Steel Structures (ÇYTHYEDY) or AISC 360-16 regulations and a connection report is created. Connection detail application limits are checked according to TBDY Table 9B.5.
In the Welded Web Connection calculation, weld access hole length and height, slip plate column cap weld thickness, slip plate beam body weld thickness and continuity plate weld thickness are checked under geometry control. In the strength control, beam shear yield, slip plate column head weld strength, column panel region slip and slip region thickness control are performed.
Connection Geometry
Geometry Checks
Weld Access Hole Length
L ≥ max(1.5tw,40 mm)
ÇYTHYEDY 13.1.6
L
50 mm
tw
9 mm
Weld Access Hole Height
H ≥ max(tw, 20 mm) , H≤50mm
ÇYTHYEDY 13.1.6
H
30 mm
tw
9 mm
Shear Plate to Column Flange Weld Size
a ≥ a min
a
9 mm
a min
3.5 mm
Table 13.4
Shear Plate to Beam Web Weld Size
a ≥ a min
a
6 mm
a min
3.5 mm
Table 13.4
a ≥ a min
a
8 mm
a min
4 mm
Table 13.4
a ≥ a min
a
8 mm
a min
4 mm
Table 13.4
Connection Detail Prequalification Limits (TBDY Table 9B.3)
Beam span / Beam cross-section height
9144 mm /450 mm=20.32
≥9.0
Beam cross-section height, d b
450 mm
≤ 920
Beam flange thickness, t bf
15 mm
≤25
Column cross section height
650 mm
≤ 920 mm
Flange plate weld
CJP
CJP
tp
10 mm
≥9 mm TBDY 9B.4.7(a)
a
10 mm
6≤a≤12 TBDY 9B.4.7 (a)
d
50 mm
≥50 mm TBDY 9B.4.7(a)
Shear plate beam web weld thickness
6 mm
=6 mm TBDY 9B.4.7(c)
Flange plate weld
CJP
CJP
Strength Checks
Beam Shear Yield
Ag
F y
275 N/mm2
Rn
ÇYTHYEDY 13.17
ΦRn
Required
Available
Ratio
Control
209.62 kN
534.6 kN
0.392
Column Flange Weld Strength at Shear Plate
Fe
490000 kN/m2
ÇYTHYEDY 13.2
in
The weld thickness taken from the combination menu is 0.707 * w value. 9 / 0.707 = 12.73 mm
l
380 mm
R req
hp
380 mm
tp
10 mm
Ry
1.30
Fyp
275 N/mm2
Rn
ΦRn
Required
Available
Ratio
Control
815.1 kN
904.94 kN
0.901
Column Panel Zone Shear
P r
429,124 kN
ÇYTHYEDY 13.29a
Py
F y
275000 kN/m2
A g
28634.759 mm2
dc
650 mm
tw
16 mm
Rn
ΦRn
Required
Available
Ratio
Control
1497.795 kN
1716 kN
0.873
Panel Zone Thickness
t min ≥u / 180
TBDY 2018 9.3.4.2b
t min = t w
16 mm
tw
16 mm
u
2016 mm
Required
Available
Ratio
Control
11.2 mm
16 mm
0.700