T Plate Connection
T plate connection is a type of non-moment-transferring connection (slip connection) that is bolted to the body of the profile and welded to the support. Bolt control, weld control and plate control are performed automatically according to the placement of the elements of the connection. Connection design with single plate is made automatically according to the Design, Calculation and Construction Principles of Steel Structures (ÇYTHYEDY) (GKT and YDKT) or AISC 360-16 (ASD and LRFD) regulations and the connection report is generated.
In the T plate connection calculation, distance control between bolts, horizontal and vertical edge distance control, weld thickness control, mounting stability controls are made as geometry control. As a strength control, checks are made for shear in the beam bolt, crushing in the beam and plate bolt holes, plate shear yielding, beam and plate shear failure, block slip in the plate, plate bending buckling, plate bending yield, support welding strength.
Connection Geometry
Geometry Checks
Bolt Spacing
ÇYTHYEDY 13.3.6
80.4 mm
20 mm
s =80.4 mm > smin = 3*20=60 mm
Horizontal Edge Distance
ÇYTHYEDY 13.3.7
40 mm
L eh ≥ 2d = 2 * 20 = 40 mm conformity check for application
26 mm
Minimum distance check according to Table 13.9
Vertical Edge Distance
ÇYTHYEDY 13.3.7
40 mm
26 mm
Weld Thickness
ÇYTHYEDY 13.3.7
9 mm
3.5 mm
Table 13.4
Erection Stability
ÇYTHYEDY 13.3.7
L
160.4 mm
190.4 mm
L=160.4 > 190.4/2=95.2 mm
Strength Checks
Bolt Shear at Beam
Ag
235.359 N/mm2
ÇYTHYEDY 13.17
Required
Available
Ratio
Control
3.67 kN
56,549 kN
0.065
Bolt Bearing on Beam
20+2=22 mm
t
6.2 mm
Required
Available
Ratio
Control
24.138 kN
107.983 kN
0.224
Bolt Bearing on Plate
20+2=22 mm
t
12 mm
ÇYTHYEDY 13.3.13
Equation 13.14a and13.14b
Required
Available
Ratio
Control
24.138 kN
180.26 kN
0.134
Beam Shear Rupture
362.846 N/mm2
ÇYTHYEDY 13.18
Required
Available
Ratio
Control
24.138 kN
129.58 kN
0.186
Plate Shear Yield
235.359 N/mm2
ÇYTHYEDY 13.17
Required
Available
Ratio
Control
24.138 kN
181.208 kN
0.133
Plate Shear Rupture
362.846 N/mm2
ÇYTHYEDY 13.18
Required
Available
Ratio
Control
24.138 kN
146,822 kN
0.164
Plate Block Shear Rupture
235.359 N/mm2
362.846 N/mm2
one
ÇYTHYEDY 13.19
Required
Available
Ratio
Control
24.138 kN
162,972 kN
0.148
Plate Flexural Buckling
Fy
235.359 N/mm2
t
12 mm
a
60 mm
L
239 mm
λ
Required
Available
Control
≤0.70
0.29
Plate Flexural Yield
278.6 mm
235.359 N/mm2
12 mm
112.95 mm
Required
Available
Ratio
Control
24.138 kN
213.295 kN
0.113
Weld Strength at Support
480000 kN/m2
in
The weld thickness taken from the combination menu is 0.707 * w value. 9 / 0.707 = 12.73 mm
362.846  N/mm2
t
12 mm
Rnw
Required
Available
Ratio
Control
0.015 kN/m
1306.245 kN/m
1.15 * 10 (-5)