Brace-Center Connection Design per AISC 360-16
How does ideCAD design brace-center connection according to AISC 360-16?
  • Brace-center connection design limit states and geometry checks are done automatically according to AISC 360-16.
Ag: Gross area
An: Net cross-section area
d: Characteristic diameter of the stem of the bolt (the diameter of the non-threaded stem of the bolt)
dh: Bolt hole diameter
t: Plate thickness
w = Size of weld leg, in. (mm)
Rn: Characteristic strength
Ubs: A coefficient considering the spread of tensile stresses
Connection Geometry
Brace-to-Gusset Plate Connection
GEOMETRY CHECKS
Bolt Spacing
The distance between the centers of bolts is checked per AISC 360-16.
smin ≥ 3d
AISC 360-16 J3.3
s
60 mm
d
20 mm
s =60 mm > smin = 3*20=60 mm
Horizontal Edge Distance
Leh ≥ L e-min
AISC 360-16 J3.4
Leh
69.85 mm
Le-min
26 mm
Vertical Edge Distance
Lev ≥ Le-min
AISC 360-16 J3.4
Lev
45 mm
Conformity check for Leh ≥ 2d = 2 * 20 = 40 mm application
Le- min
26 mm
Weld Size
w ≥ wmin
AISC 360-16 J2.4
w
5.658 mm
wmin
5 mm
Table J2.4
STRENGTH CHECKS
Bolt Shear at Brace
The bolt shear limit state of the connection is checked according to AISC 360-16.
Ab
Fn
Rn
AISC 360-16 J3-1
ΦRn
Required
Ready
Rate
Control
205.872 kN
212.058 kN
0.971
Bolt Bearing on Plate
The bearing strength limit states of the connection plate, which are “shear tear out” and “ovalization of bolt hole” for both end and inner bolts, are checked according to AISC 360-16.
dh
20+2=22 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Ready
Rate
Control
205.872 kN
456.84 kN
0.451
Bolt Bearing on Gusset
dh
20+2=22 mm
Lc,edge
Rn
AISC 360-16 J3-6a
Rn-edge
Lc,spacing
Rn-spacing
Rn
ΦRn
Required
Ready
Rate
Control
205.872 kN
304.56 kN
0.676
Weld Strength
The nominal and design strength of the weld is checked according to AISC 360-16
Fe
490000 kN/m2
w
5.658 mm
Fu-plate
469.999  N/mm2
Fu-brace
410 N/mm2
tplate
15 mm
AISC 360-16 J3-6a
tbrace
15 mm
lw
150 mm
Rnw
Rn-plate
RnBM
Rn
ΦRn
Required
Ready
Rate
Control
205.872 kN
529.2 kN
0.389
Whitmore Section Compression Yield
The buckling limit state in withmore section of the plate subjected to compression is checked according to AISC 360-16.
K
0.65
L
0 mm
r
2.887 mm
KL / r
0
Fy
355 N/mm2
Ag
1292.82 mm2
Rn
AISC 360-16 J4-6
ΦRn
Required
Ready
Rate
Control
205.872 kN
413.056 kN
0.498